Long time coming, it's finally here and working well. You can now control your ULTI Zigbee Switches from Can2Go. Actually, by this method, you will be able to control any Zigbee device that supports the Zigbee Cluster Library. (Yes, that pretty much includes most of the LifeSpace stuff in APAC and EMEA).
What will you need to do this:
-- 24V. Power Supply
-- 1 UN2/SSL/Can2Go/MPM (or whatever you want to call it)
-- At least one ULTI Zigbee Switch connected to some sort of lighting
First you need to create the Zigbee network on the UN2. Login to the UN (default is admin/admin), select it in the tree, then on the right click on Zigbee Configuration.
You can use the settings bellow and don't worry about the Extended Network ID as we'll overwrite it anyway.
A few comments/highlights:
Awesome! Click Save and the network status should change to "formed".
Next, you need to create a Lua script in order to control our ULTI devices.
Click the Add Objects button (first button in the toolbar). In the new windows, set the Filter to "Lua Program". Finally add a Lua Script.
First of all, we'll need to reset the Extended Pan Id in our script.
In order for some of the Schneider products to work with your UN2, they need to have a specific extended Pan Id. It needs to be 0x10,0x5E,0x01,0x04,0x45,0x48,0xYY,0xYY where YY can be any valid hexadecimal value.
So in Lua, it comes to:
if PG1_Init == nil then
ME.ZBC1_Pan_Ext.value = string.char(0x5E,0xD3,0x48,0x45,0x04,0x01,0x5E,0x10)
...
Let's look at the script in details:
1. Declaration
lights = {
{"00124B0001CA0F05", 11, "BV2"}, -- 2-Gang Dimmer
{"00124B00017B19C0", 10, "BV4"}, -- 1-Gang Switch
{"00124B0002925A40", 10, "BV6"} -- 2-Gang Switch
}
This is where you declare all the lights that you want to connect to and control. Each light has three parameters:
2. The Lua functions
Next you will need 3 main commands:
3. Start up
At startup, you will have a few declarations. The status array is used to store the current values of the lights while the lastToggle keeps the timestamp of the last time it was turned on/off. This is used to ignore some of the received commands for the lights as all the messaging is asynchronous.
Finally, to make it look nicer, you can actually create a Dashboard using a switch and linking it to your BV value.
As you will notice, the commands are using the standard Zigbee Cluster Library (ZCL). For on/off, we are using the on/off cluster (0x0006). In order to do dimming, you will need to implement another cluster (my guess is the Level Control Cluster?). We are currently trying it and will keep you updated! Just like this post for an update! 🙂
Final thing, you will need to join your device/switch to the Zigbee network. To do so, it's real easy, in the Zigbee Configuration of your UN2, check the "Permit Join Broadcast" box. Then on your switch press the Prog button. Wait a few seconds. The small light indicator on your switch should change from orange to green. Once this is done, make sure to uncheck "Permit Join Broadcast" and if the light is still green on the switch, close the Zigbee network by pressing the Prog button again.
That's it!
If you have any question/comment, don't hesitate!
Link copied. Please paste this link to share this article on your social media post.
Hi Laurent,
I have tried the above methods by replacing the extended id and tie to bv4 for on/off function. I have also set the settings for MPM zigbee config. Anything else I miss? Do I have to call out the 3 commands? If yes, how do I call?
Thanks.