Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

COMX Replacement scenario / EO pre-configuration

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • COMX Replacement scenario / EO pre-configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Romain_Polette Champion
128
Guillaume_Evrard
Guillaume_Evrard Leader
60
Eric_HAVAS
Eric_HAVAS Leader
49
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
pbrunot
pbrunot Leader
Leader

Posted: ‎2013-11-15 04:46 AM

2 Likes
3
1333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-15 04:46 AM

COMX Replacement scenario / EO pre-configuration

Hello,

We're evaluating the COMX as a replacement of EGX300 for a large number of submetering kits sold to ENEL (large Utility company in Italy).  The gateway is used to push data to Energy Operation portal.

Energy Operation portal also receives metered data from billing system of ENEL (it's not only made of submetering kits).We're dealing with 100's of kits now and plan to sell 1000's next year in this model.

For many practical reasons we cannot preconfigure COMX for a given site before to ship them to end-users (endusers order them in bulk and give it to third party companies for installation). So the project team must give configuration instructions to installers, and prepare EO accordingly, so that activation goes smoothly with minimal =S= involvement.

We're doing office tests with COMX and have come to the following conclusions :

1- The DeviceID used by the COMX is non-editable and generated randomly.

2- DeviceID is not printed so it cannot be known before device is installed / powered on
3- Since this deviceid is used to push data in EO, if it changes, the upload mechanism breaks: the hierarchy can be resent to EO after device id change, but this results in new meters being created (not merged).

4- Since automatically created hierarchy cannot be set to match the existing hierarchy in EO, we must reconfigure the pushed hierarchy in EO for every meter.

We'd like to know if points 1, 2 and 3 are correct.

With EGX, we had to create from scratch the hierarchy in EO, but we were able to configure everything in EO before the EGX shipped : this because since we assigned device ID (based on site spatial hierarchy in EO) in the configuration instructions for the installers. With EGX, installers could install & configure everything and see the data in EO one hour after.

So we think the new DeviceID model creates some issues in our deployment scenario :

a. If a COMX needs replacement, there's no way to give it the old device id -> must rework the configuration in EO and historical data is lost (new meters)

b. With COMX, the deviceid is unknown until it is powered on -> we cannot pref-config EO, only configure EO only after device installation in the field.

Did we miss something? Any known workarounds for these issues ?

Thanks for your support!


Tags (3)
  • Tags:
  • comx
  • egx
  • energy_operation
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2013-11-20 06:48 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-20 06:48 AM

Point 1, 2 and 3 are correct :

1- The DeviceID used by the COMX is generated randomly.

2- DeviceID is not printed so it cannot be known before device is installed / powered on
3- Since this deviceid is used to push data in EO, if it changes, the upload mechanism breaks: the hierarchy can be resent to EO after device id change, but this results innew meters being created (not merged).

The only think I can add is that the site ID is displayed in the "General settings / publication" tab.

Point a can be completed a little bit : If you have saved the configuration of a Com'X 200 "A" (and saved the configuration file on your PC) ,

When you will restore this configuration to a Com'X 200 "B", this last one will get the ID of "A" .

This behaviour has been defined in order to suport the "Faulty Device Replacement" usecase

If you want to clone the Com'X 200 "A" on B", (but for another site), you have to click on the "Generate New Publication ID" button before to restart the periodic publication

(That's why the periodic publication is not restarted automaticaly after a configuration restore)

See Answer In Context

Reply
Replies 3
Anonymous user
Not applicable

Posted: ‎2013-11-15 05:37 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-15 05:37 AM

Hello Pascal,

I will let the experts respond more accurately but here are some feedbacks after several months of use of Com'X in an old French administrative building (R&D project) :

We've installed 5 Com'X connected to about 200 physical sensors (each one sending 5 measurments). Com'X also export to EO.

To my point of view, your first 3 points are correct.

For point 4 what we did is just ignore the hierarchy pushed by the Com'X :

     - after the first publication of the hierarchy (topology.xml), in EO all the meters were relocated under the default SITE_NEWMETERS site => we had to process again our own hierachy commissioning file from EO UI.

     - then the hierachy should not be exported again by the Com'X (in previous release, it was still the case after each reboot..)

For point a. we deal with ComX save/restore configuration.

For point b. I agree : you can pre-config in EO the hierarchy but not the meters (need to know the DeviceID).

We also expermented a "self hand made third party tool" in order to generate Com'X configuration.

Dimitri.

Reply
Anonymous user
Not applicable

Posted: ‎2013-11-20 06:48 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-20 06:48 AM

Point 1, 2 and 3 are correct :

1- The DeviceID used by the COMX is generated randomly.

2- DeviceID is not printed so it cannot be known before device is installed / powered on
3- Since this deviceid is used to push data in EO, if it changes, the upload mechanism breaks: the hierarchy can be resent to EO after device id change, but this results innew meters being created (not merged).

The only think I can add is that the site ID is displayed in the "General settings / publication" tab.

Point a can be completed a little bit : If you have saved the configuration of a Com'X 200 "A" (and saved the configuration file on your PC) ,

When you will restore this configuration to a Com'X 200 "B", this last one will get the ID of "A" .

This behaviour has been defined in order to suport the "Faulty Device Replacement" usecase

If you want to clone the Com'X 200 "A" on B", (but for another site), you have to click on the "Generate New Publication ID" button before to restart the periodic publication

(That's why the periodic publication is not restarted automaticaly after a configuration restore)

Reply
sesa24896
sesa24896 Leader
Leader

Posted: ‎2013-11-21 12:33 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-11-21 12:33 AM

Hi Pascal

We are currently working with Marco Melato's team to provide a tool (feb 2014) that will generate automatically a Com'X configuration file with the same parameters entered by the installer than the ones in the excel sheet. The POD of Enel contract will then be used for the publication ID

You can talk to Marco directly to get more info

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore