DCE Sensor Mapping to ITA

For DCIM developers

EcoStruxure IT Advisor integrations for the advanced user

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • For DCIM developers
  • For DCIM developers
  • DCE Sensor Mapping to ITA
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • IT Advisor REST API
  • Debugging issues with DCE DDF files in EcoStruxure...
  • Web proxy configuration for the ITA web client or ...
  • DCE Sensor Mapping to ITA
  • DCE web services API
  • IT Advisor REST API
  • Debugging issues with DCE DDF files in EcoStruxure...
  • Web proxy configuration for the ITA web client or ...
  • DCE Sensor Mapping to ITA
  • DCE web services API

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to For DCIM developers
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2670 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DCE Sensor Mapping to ITA

Picard EcoStruxureIT
‎2020-03-18 02:12 AM

ITA uses the standard web services to query Data Center Expert for device and sensor related data.

Device Information

To get device information, this information from the DCE web interface /integration/services/ISXCentralDeviceService_v2_0?wsdl is used:

<xsd:complexType name="ISXCDevice">
<xsd:sequence>
<xsd:element name="ISXCNamedElement" nillable="true" type="ns2:ISXCNamedElement"/>
<xsd:element name="ISXCCommState" nillable="true" type="ns2:ISXCCommState"/>
<xsd:element name="ISXCDeviceType" nillable="true" type="ns2:ISXCDeviceType"/>
<xsd:element minOccurs="0" name="hostName" nillable="true" type="xsd:string"/>
<xsd:element minOccurs="0" name="ipAddress" nillable="true" type="xsd:string"/>
<xsd:element name="location" nillable="true" type="xsd:string"/>
<xsd:element minOccurs="0" name="modelName" nillable="true" type="xsd:string"/>
<xsd:element minOccurs="0" name="modelNumber" nillable="true" type="xsd:string"/>
<xsd:element name="parentID" nillable="true" type="xsd:string"/>
<xsd:element minOccurs="0" name="serialNumber" nillable="true" type="xsd:string"/>
<xsd:element name="ISXCDeviceState" nillable="true" type="ns2:ISXCDeviceState"/>
<xsd:element minOccurs="0" name="supplemental" nillable="true" type="xsd:string"/>
</xsd:sequence>
<xsd:attribute name="isPrivate" type="xsd:boolean"/>
</xsd:complexType>

Note

The supplemental string is mandatory to understand the nature of the device.

For example, for power related devices, phase and bank information is present in the supplemental string used in ITA to create an object of the device.

Example of  PDU with 1 phase and 2 banks:

<ns2:supplemental>InputPhaseCount="1";OutputPhaseCount="1";BankCount="2"</ns2:supplemental>

 


Sensor Information

A number of sensors are also used from the DCE web service interface /integration/services/ISXCentralSensorService_v2_0?wsdl

To create an object to be used for the sensors, use:

Note

Index is being used to identify which module and phase are reporting data.

That means index must be unique across sensorType on a given device

 

It is NOT allowed to have e.g. 2 sensors of the same sensorType reporting same index. For example a single phase rack PDU with 2 banks and reporting phase information as well. Same sensorType having same index:

This is NOT allowed

<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>
<ns2:id>B717125_nbSNMPEncEC23C4AA_RPDU_OUTPUT_POWER_BANK_1</ns2:id>
<ns2:index>1</ns2:index>
<ns2:ISXCSensorType>OUTPUT_POWER_WATTS</ns2:ISXCSensorType>


<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>


<ns2:id>B717125_nbSNMPEncEC23C4AA_RPDU_PHASE_OUTPUT_POWER_1</ns2:id>
<ns2:index>1</ns2:index>
<ns2:ISXCSensorType>OUTPUT_POWER_WATTS</ns2:ISXCSensorType>

To get the above example right, the phase output power should be reported as OUTPUT_POWER_TOTAL_WATTS (which does not use index).

Single phase devices with no banks should only use the OUTPUT_POWER_TOTAL_WATTS sensorType.

From the ISXCSensorType, a subset of the sensors are mapped in ITA for temperature, humidity, and power.

Temperature Sensors:

EXTERNAL_TEMPERATURE

SUPPLY_AIR_TEMPERATURE

RETURN_AIR_TEMPERATURE

INTEGRATED_TEMPERATURE

RACK_INLET_TEMPERATURE

UNIT_TEMPERATURE

Humidity Sensors:

EXTERNAL_HUMIDITY

SUPPLY_AIR_HUMIDITY

RETURN_AIR_HUMIDITY

INTEGRATED_HUMIDITY

UNIT_HUMIDITY

Power Sensors:

OUTPUT_POWER_WATTS

OUTPUT_POWER_TOTAL_WATTS

MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER

Amp Sensors:

MODULE_BREAKER_CURRENT

OUTPUT_CURRENT

OUTPUT_CURRENT_TOTAL

INPUT_CURRENT

 

The SensorType is ignored when using sensor mapping functionality at PDU level.

Tip

Power sensors used for Modular PDU / Branch Circuit Monitoring

For a modular PDU/Branch Circuit Monitoring, the MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER are the sensors used to get power data from the device.

 

An example of a modular PDU with 3 phases and 24 breaker modules:

At device level, the "supplemental" string is used to specify number of phases and breaker modules.

 

<ns2:supplemental>InputPhaseCount="3";OutputPhaseCount="3";BankCount="24"</ns2:supplemental>


At sensor level, the sensorType is used to specify a modular PDU reporting data and the index is used to identify the phase reporting on a module. In this example breaker module 5, phase 3 (index 5,3):

<ns2:ISXCSensorType>MODULE_OUTPUT_POWER</ns2:ISXCSensorType>
<ns2:index>b,p</ns2:index> - e.g. <ns2:index>5,3</ns2:index>

Data Collection

The data collected from DCE via the power sensors is Peak and Average data. Peak and Average power data is queried for an interval of one day, 1 time/day. Additionally, peak power data is queried every 5 minutes since last time queried.

We store the data and calculate Peak and Average values based on a setting in the ITA server (10, 20, 30 days).

 

Summary

The expected values used to specify and map the device in ITA:

ISXCDevice - Supplemental ISXCSensor
PhaseCount BankCount Index SensorType Device example
1 1 Ignored OUTPUT_POWER_TOTAL_WATTS rack PDU
1 >1 1 digit = Bank number OUTPUT_POWER_WATTS rack PDU with banks
1 - Ignored OUTPUT_POWER_TOTAL_WATTS  
3 1 1 digit = Phase number OUTPUT_POWER_WATTS UPS or (RM)PDU
3 >1 2 digit = Module, Phase MODULE_OUTPUT_POWER Modular PDU
3 - 1 digit = Phase number OUTPUT_POWER_WATTS  

 

Note

Supplemental is mandatory and must include phase information

PhaseCount references InputPhaseCount and OutputPhaseCount which is expected to be the same number.

DCE exposes information through various web services.

For device information, ITA uses:

getAllDeviceGroups

getDevicesForGroupID

 

For sensor information and data, ITA uses: 

getSensorsByType

getMultipleAverageSensorData

getMultiplePeakSensorData

Verifying DDFs with Soap-UI

The walkthrough below is done with SoapUI 5.4.0. You can download the latest version here: https://www.soapui.org/

When setting up a new project, chose the SOAP project type.

Screenshot1_360006754317.pngScreenshot1_360006754317.png

The initial WSDL link should be

http://X.X.X.X/integration/services/ISXCentralDeviceService_v2_0?wsdl for the device endpoint.

http://X.X.X.X/integration/services/ISXCentralSensorService_v2_0?wsdl for the sensor endpoint.

Where X.X.X.X is ip address for the DCE server.

Screenshot2_360006754317.pngScreenshot2_360006754317.png

When prompted for the username and password, provide those used for logging into the DCE server.

Running a request against the DCE server

When running a request against the endpoint, first choose the endpoint in the list, and fold out so you can see the sample request.

Screenshot3_360006754317.pngScreenshot3_360006754317.png

Before running the request, you need to setup authentication:

  1. Chose 'Basic'
  2. Enter in the username and password for the DCE server

Screenshot4_360006754317.pngScreenshot4_360006754317.png

Then press play to run the request.

Dependent on the request it might be necessary to fill in a number of parameters.

When you have identified the correct device use the sensor end point to ensure that sensors with the correct type are available.

Running requests to verify sensors with the correct type are available

Getting the sensors for a specific device.

Several of the end point are of interest, this is just an example on one why to do the verification.

Given an ID for a device, all the sensors for the device can be gathered with the getSensorsForDevice request.

Screenshot5_360006754317.pngScreenshot5_360006754317.png

Fill in the ID for the device

Screenshot6_360006754317.pngScreenshot6_360006754317.png

Check that sensors with the types mentioned in the first part of this document are present. One example for the OUTPUT_POWER_WATTS sensor type is shown below.

Screenshot7_360006754317.pngScreenshot7_360006754317.png

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore