Configuring Data Center Expert integration

External system integration (on premises only)

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA installation and setup
  • External system integration (on premises only)
  • Configuring Data Center Expert integration
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to External system integration (on premises only)
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1613 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Data Center Expert integration

Picard EcoStruxureIT
‎2019-10-14 08:34 AM

For IT Advisor on-premise installations only
NOTE: Hosted ITA integrates with IT Expert only. 
Configure the server connection to allow IT Advisor to communicate with the Data Center Expert server and receive device data and alarms.

It is possible to integrate with multiple Data Center Expert servers.

  1. Select System Setup > External System Configuration.
  2. Click Add server, and select Data Center Expert as the server type.
  3. Type the Data Center Expert server identification, such as name, IP, port (80 or 443), and credentials.
  4. To configure the data collection settings (see screenshot), set:
    • Time period for calculation of peak and average power values (Calculate power data based on the last).
    • Interval for asking Data Center Expert for updated device data (temperatures are collected).
    • Interval for asking Data Center Expert for updated power data. (This value does not include all kW measurements. Power data from rack PDUs is collected, whereas power data from cooling units is not.)
    • Full alarm synchronization every (how often IT Advisor synchronizes alarms and alarm statuses from Data Center Expert).
    • Retrieve sensors: If you select this, data from sensors such as temperature sensors are included. If you do not want to see the temperature sensor data in IT Advisor, do not select this.
    • Callback information to the IT Advisor server. This is used to tell Data Center Expert which ip/hostname to push alarms once they occur.
      • To Use Encryption a certification must be added to Data Center Expert. See Configuring a secure connection below.
    • Timeout settings for connection and response.
      • Stop trying to connect after: In case IT Advisor cannot connect to the Data Center Expert server, the user will get a warning after the specified amount of time, and data collection will resume when the connection has been restored.
      • Stop waiting for data after: IT Advisor will drop the connection after the specified time to avoid having a hanging connection.
  5. When you have finished the steps in the wizard and the server has been added to the list of external systems, click Test to test the connection.

 

DCE_ITA_option_360036883094.pngDCE_ITA_option_360036883094.png

Configuring a secure connection

If you want to ensure a secure connection for the data exchanged between the systems, follow these instructions to ensure the certificate is trusted on both Data Center Expert and IT Advisor servers.

  1. Access the IT Advisor server management interface to access the certificate.
    1. Launch the Webmin web interface by typing the address of the IT Advisor server in a Web browser and click Server Configuration.
    2. Log on to Webmin using the user credentials created during the installation.
    3. In the Webmin interface menu, select System>Upload and Download.
    4. Open the Download from server tab.
    5. Browse to the certificate: /etc/isx-operations/ssl/certificate.crt and click Download.
    6. Open the .crt file with a text editor, such as Notepad.
    7. Select all and copy the contents (Ctrl+A/Ctrl+C).
      Alternatively, in a web browser:
      a. Type the server IP address and click the pad lock icon to the left to open View Site Information.
      b. Click Certificate Information.
      c. In the Connection tab, click Export and save as .pem.
      d. Open the file to copy the contents.
      For Mac, there's an extra Keychain step before exporting, see animation.
  2. Make the certificate available to Data Center Expert.
    1. Launch Data Center Expert.
    2. Select System>Server Administration Settings>Server SSL Certificates...
    3. Click Add..., right-click and select Paste to paste in the contents of the .crt file (from above step), and click Add.
      The connection has been set up and the certificate is trusted on both servers.

Access and copy contents from certificate. This example uses Chrome on Mac.

105470281_854x250_360036883094.gif105470281_854x250_360036883094.gif

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore