Untuk MiCOM P122, maksudnya Time Tolerance operasional untuk ambang batas I>, I>> dan I>>> adalah +/- 2% +30...50ms.?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Untuk MiCOM P122, maksudnya Time Tolerance operasional untuk ambang batas I>, I>> dan I>>> adalah +/- 2% +30...50ms.?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-09-29 08:11 AM

0 Likes
4
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-29 08:11 AM

Untuk MiCOM P122, maksudnya Time Tolerance operasional untuk ambang batas I>, I>> dan I>>> adalah +/- 2% +30...50ms.?

Saya ada pertanyaan mengenai MiCOM P122.

Dalam manual relai disebutkan bahwa Time Tolerance operasional untuk ambang batas I>, I>> dan I>>> adalah +/- 2% +30...50ms. Oleh karena itu, apakah benar bahwa toleransi negatif untuk kurva yang ditetapkan adalah 2% dari nilai yang ditetapkan. Begitupun untuk toleransi positif untuk kurva yang ditetapkan adalah 2% dari nilai yang ditetapkan ditambah 50ms? Terima kasih.

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Fikri_Ferdiana
Ensign Fikri_Ferdiana Ensign
Ensign

Posted: ‎2021-09-30 12:47 AM

1 Like
3
1190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-30 12:47 AM

Hi Pak @Anonymous user ,

 

Nilai time tolerance yang dimaksud adalah akurasi waktu kerja proteksi Overcurrent (I>, I>>, I>>>)  berdasarkan nilai setting waktu yang ditentukan.

 

Sebagai contoh kita menggunakan setting definite time 100 ms.

Maka waktu kerja proteksi yang sebenarnya adalah 100 ms +/- 2% +30...50 ms => antara 98 ms sampai 150 ms.

Nilai +2% digunakan mana yang lebih besar dengan 50 ms dikalikan setting waktu.

 

Semoga cukup jelas.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Fikri_Ferdiana
Ensign Fikri_Ferdiana Ensign
Ensign

Posted: ‎2021-09-30 12:47 AM

1 Like
3
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-30 12:47 AM

Hi Pak @Anonymous user ,

 

Nilai time tolerance yang dimaksud adalah akurasi waktu kerja proteksi Overcurrent (I>, I>>, I>>>)  berdasarkan nilai setting waktu yang ditentukan.

 

Sebagai contoh kita menggunakan setting definite time 100 ms.

Maka waktu kerja proteksi yang sebenarnya adalah 100 ms +/- 2% +30...50 ms => antara 98 ms sampai 150 ms.

Nilai +2% digunakan mana yang lebih besar dengan 50 ms dikalikan setting waktu.

 

Semoga cukup jelas.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-09-30 11:30 PM

In response to Fikri_Ferdiana
0 Likes
2
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-30 11:30 PM

jadi misalkan settingan di 100 ms, maka:
- Untuk toleransi negatifnya --> 100 ms - 2% x 100 ms = 100 ms - 2 ms = 98 ms
- Untuk toleransi positifnya --> karena 2% dari 100 ms, maka menggunakan 50 ms, sehingga --> 100 ms + 50 ms = 150 ms

Begitu ya Pak @Fikri_Ferdiana ?

 

Terima kasih.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Fikri_Ferdiana
Ensign Fikri_Ferdiana Ensign
Ensign

Posted: ‎2021-10-01 12:22 AM

In response to Anonymous user
0 Likes
1
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-01 12:22 AM

Betul pak @Anonymous user 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-05 09:22 PM

In response to Fikri_Ferdiana
0 Likes
0
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-05 09:22 PM

Paham Pak @Fikri_Ferdiana . Berarti untuk toleransi negatif pakai yang 2%, sedangkan untuk toleransi positif pakai 2% atau 50 ms, lebih besar yang mana ya.

Terima kasih banyak atas infonya!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore