Pemilihan Konduktor - Kabel atau Busway / Busduct

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Pemilihan Konduktor - Kabel atau Busway / Busduct
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
KKS
Ensign KKS
Ensign

Posted: ‎2022-08-17 10:44 PM

1 Like
4
2590
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-17 10:44 PM

Pemilihan Konduktor - Kabel atau Busway / Busduct

Mohon diberikan penjelasan mengenai pemilihan konduktor apakah lebih baik menggunakan kabel atau menggunakan Busbar (Busway / Busduct).\

 

Apa saja kelebihan menggunakan Busway / Busduct dibandingkan kabel ?

Labels
  • Labels:
  • Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-08-22 01:14 AM

2 Likes
1
2567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-22 01:14 AM

Berikut saya tambahkan beberapa point untuk keuntungan dari sistem trunking busway dibandingkan kabel, penjabarannya adalah sebagai berikut:

 

Keleluasaan/flexibilitas

  • Konfigurasi yang mudah diubah (modifikasi di tempat untuk mengubah konfigurasi lini produksi atau memperluas area produksi).
  • Menggunakan kembali komponen (komponen tetap utuh): ketika instalasi dapat dimodifikasi besar, trunking busbar mudah dibongkar dan digunakan kembali.
  • Ketersediaan daya di seluruh instalasi (kemungkinan memiliki titik tap-off setiap meter).
  • Berbagai pilihan unit tap-off.

Kemudahan

  • Desain dapat dilakukan secara independen dari distribusi dan tata letak konsumen saat ini.
  • Kinerja tidak tergantung pada implementasi: penggunaan kabel membutuhkan banyak koefisien derating.
  • Hapus tata letak distribusi
  • Pengurangan waktu pemasangan: sistem trunking memungkinkan waktu pemasangan dikurangi hingga 50% dibandingkan dengan pemasangan kabel tradisional.
  • Jaminan produsen
  • Waktu eksekusi terkontrol: konsep sistem trunking menjamin bahwa tidak ada kejutan yang tidak terduga saat pemasangan. Waktu pemasangan diketahui dengan jelas sebelumnya dan solusi cepat dapat diberikan untuk setiap masalah di lokasi dengan peralatan yang dapat beradaptasi dan dapat diskalakan ini.
  • Mudah diimplementasikan: komponen modular yang mudah ditangani, sederhana dan cepat terhubung.

Kehandalan

  • Keandalan dijamin dengan dibangun di pabrik
  • Unit yang sangat mudah
  • Perakitan berurutan dari komponen lurus dan unit tap-off sehingga tidak mungkin membuat kesalahan apa pun

Kontinuitas layanan

  • Banyaknya titik tap-off memudahkan untuk memasok daya ke konsumen baru saat ini. Menghubungkan dan memutuskan sambungan cepat dan dapat dilakukan dengan aman bahkan ketika diberi energi. Kedua operasi ini (menambah atau memodifikasi) berlangsung tanpa harus menghentikan operasi.
  • Pemeliharaan tidak ada atau minim aktifitas maintenance

 

Efek terhadap Lingkungan

  • Sistem trunking busbar memungkinkan sirkuit digabungkan. Dibandingkan dengan sistem distribusi kabel tradisional
  • Perangkat yang dapat digunakan kembali dan semua komponennya sepenuhnya dapat didaur ulang
  • Tidak mengandung PVC dan tidak menghasilkan gas atau limbah beracun.
  • Pengurangan risiko karena paparan medan elektromagnetik

 

Minim resiko terhadap kejadian kebakaran yang disebabkan korsleting listrik

Busway dapat membantu desainer mengatasi risiko kebakaran listrik yang dapat ditimbulkan oleh konduktor

 

Kenaikan suhu busway dan tahan hubung singkat diketahui dan independen dari instalasi, mereka diuji dan disertifikasi sesuai dengan standar IEC 61439-6. Selain itu, koordinasi pemutus sirkuit dan busway Schneider Electric memastikan ukuran yang dioptimalkan dengan perlindungan sempurna terhadap kondisi hubung singkat. Selain itu, untuk sirkuit arus tinggi, beberapa kabel secara paralel dapat menyebabkan distribusi arus yang tidak merata dan risiko kenaikan suhu yang tidak normal. Standar pemasangan IEC 60364- 5-52 Klausul 523.7 merekomendasikan sistem trunking busbar (busway) di atas empat kabel paralel

 

IEC 60364-4-42 2010 422.3 yang disebutkan sebelumnya, menyatakan bahwa busbar tidak perlu dilindungi oleh 300mA RCD di lokasi dengan risiko kebakaran khusus, karena mereka tidak dianggap mungkin menyebabkan kebakaran dari kesalahan isolasi

 

Semoga uraian diatas membantu 

 

Salam,

Faisal

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-08-18 02:32 AM

0 Likes
1
2585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-18 02:32 AM

@Nedi 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-08-19 01:36 AM . Last Modified: ‎2022-08-19 01:44 AM

In response to HelvinHermanT
0 Likes
0
2574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-19 01:36 AM . Last Modified: ‎2022-08-19 01:44 AM

Busway vs Cable.jpg

 

Saat tuntutan kapasitas distribusi besar dan tempat terbatas, kita bisa menggunakan Busway / Busduct.

 

Bisa dilihat dari foto diatas perbandingan dimensi antara Busway/Busduct dengan Kabel. Dimensi Busway lebih praktis dan efisien dibandingkan dengan kabel.

 

Bisa kita banyangkan biaya pemasangan yang dibutuhkan untuk memasang kabel pastinya lebih besar dan lebih lama. Untuk pemasangan kabel dibutuhkan kabel ladder atau kabel tray untuk menempatkan kabel, membutuhkan kabel gland dan terminal untuk koneksi.

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-08-22 01:14 AM

2 Likes
1
2568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-22 01:14 AM

Berikut saya tambahkan beberapa point untuk keuntungan dari sistem trunking busway dibandingkan kabel, penjabarannya adalah sebagai berikut:

 

Keleluasaan/flexibilitas

  • Konfigurasi yang mudah diubah (modifikasi di tempat untuk mengubah konfigurasi lini produksi atau memperluas area produksi).
  • Menggunakan kembali komponen (komponen tetap utuh): ketika instalasi dapat dimodifikasi besar, trunking busbar mudah dibongkar dan digunakan kembali.
  • Ketersediaan daya di seluruh instalasi (kemungkinan memiliki titik tap-off setiap meter).
  • Berbagai pilihan unit tap-off.

Kemudahan

  • Desain dapat dilakukan secara independen dari distribusi dan tata letak konsumen saat ini.
  • Kinerja tidak tergantung pada implementasi: penggunaan kabel membutuhkan banyak koefisien derating.
  • Hapus tata letak distribusi
  • Pengurangan waktu pemasangan: sistem trunking memungkinkan waktu pemasangan dikurangi hingga 50% dibandingkan dengan pemasangan kabel tradisional.
  • Jaminan produsen
  • Waktu eksekusi terkontrol: konsep sistem trunking menjamin bahwa tidak ada kejutan yang tidak terduga saat pemasangan. Waktu pemasangan diketahui dengan jelas sebelumnya dan solusi cepat dapat diberikan untuk setiap masalah di lokasi dengan peralatan yang dapat beradaptasi dan dapat diskalakan ini.
  • Mudah diimplementasikan: komponen modular yang mudah ditangani, sederhana dan cepat terhubung.

Kehandalan

  • Keandalan dijamin dengan dibangun di pabrik
  • Unit yang sangat mudah
  • Perakitan berurutan dari komponen lurus dan unit tap-off sehingga tidak mungkin membuat kesalahan apa pun

Kontinuitas layanan

  • Banyaknya titik tap-off memudahkan untuk memasok daya ke konsumen baru saat ini. Menghubungkan dan memutuskan sambungan cepat dan dapat dilakukan dengan aman bahkan ketika diberi energi. Kedua operasi ini (menambah atau memodifikasi) berlangsung tanpa harus menghentikan operasi.
  • Pemeliharaan tidak ada atau minim aktifitas maintenance

 

Efek terhadap Lingkungan

  • Sistem trunking busbar memungkinkan sirkuit digabungkan. Dibandingkan dengan sistem distribusi kabel tradisional
  • Perangkat yang dapat digunakan kembali dan semua komponennya sepenuhnya dapat didaur ulang
  • Tidak mengandung PVC dan tidak menghasilkan gas atau limbah beracun.
  • Pengurangan risiko karena paparan medan elektromagnetik

 

Minim resiko terhadap kejadian kebakaran yang disebabkan korsleting listrik

Busway dapat membantu desainer mengatasi risiko kebakaran listrik yang dapat ditimbulkan oleh konduktor

 

Kenaikan suhu busway dan tahan hubung singkat diketahui dan independen dari instalasi, mereka diuji dan disertifikasi sesuai dengan standar IEC 61439-6. Selain itu, koordinasi pemutus sirkuit dan busway Schneider Electric memastikan ukuran yang dioptimalkan dengan perlindungan sempurna terhadap kondisi hubung singkat. Selain itu, untuk sirkuit arus tinggi, beberapa kabel secara paralel dapat menyebabkan distribusi arus yang tidak merata dan risiko kenaikan suhu yang tidak normal. Standar pemasangan IEC 60364- 5-52 Klausul 523.7 merekomendasikan sistem trunking busbar (busway) di atas empat kabel paralel

 

IEC 60364-4-42 2010 422.3 yang disebutkan sebelumnya, menyatakan bahwa busbar tidak perlu dilindungi oleh 300mA RCD di lokasi dengan risiko kebakaran khusus, karena mereka tidak dianggap mungkin menyebabkan kebakaran dari kesalahan isolasi

 

Semoga uraian diatas membantu 

 

Salam,

Faisal

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-08-23 03:15 AM . Last Modified: ‎2022-08-23 03:27 AM

In response to faisalamir
1 Like
0
2561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-23 03:15 AM . Last Modified: ‎2022-08-23 03:27 AM

Mantap Pak @faisalamir .

 

Saya cek di PUIL 2020 bagian 4-42 yang diadopsi dari IEC 60364-4-42 memang menyebutkan demikian.

 

IEC 60364-4-42 2010 422.3 yang disebutkan sebelumnya, menyatakan bahwa busbar tidak perlu dilindungi oleh 300mA RCD di lokasi dengan risiko kebakaran khusus, karena mereka tidak dianggap mungkin menyebabkan kebakaran dari kesalahan isolasi

 

RCD Busbar 1.jpg

 

Terima kasih

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.