IEC 61439
Expert on Demand for Standards & Regulations
Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.
  • Power Distribution IEC
  • IEC 61439
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
VickyTanzil
Ensign VickyTanzil Ensign
5
Back to Expert on Demand for Standards & Regulations
Posted: ‎2021-10-23 03:36 AM
926
IEC 61439
Is there any guideline as per IEC-61439 equivalent to PTTA specification of IEC-60439 or IS-8623 that earlier we referred for panel / DBs ?
  • India
Posted: ‎2021-10-26 12:55 AM
Hi Sudhansu
The concept of TTA & PTTA are no more relevant in IEC61439. TTA & PTTA are replaced by design verifications.
An Switchboard manufacturer obliged to prove the performance and constructional characteristic by either
  1. Testing
  2. Comparison with a reference design
  3. Assessment
Comprehensive guidelines for each and every characteristics are very well defined in IEC61439-1 Edition 3 . For example, refer Annex L for temperature rise performance verification and refer Table 13 + Annex M for short circuit performance evaluation. Similar guidelines are also furnished for all the relevant characteristics for the corresponding performance evaluation and assessment.
Do revert back in case if you seek further details.
Regards
S.Saravanan
Principal Technical Expert