IEC 61439

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • IEC 61439
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Expert on Demand for Standards & Regulations
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-07-20 12:03 AM

0 Likes
3
1984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 12:03 AM

IEC 61439

Is there any exceptions in IEC61439, which states that the short circuit tests are not required. If so, can you elaborate and quote those clauses.

Labels
  • Labels:
  • India
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Anonymous user
Not applicable

Posted: ‎2021-07-20 02:39 AM

1 Like
1
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 02:39 AM

IEC61439-1 doesn't warrant for short circuit performance evaluation under the following conditions:

 

  1. Assemblies protected by short circuit protective devices whose cut off current is not more than 17kA with prospective current set at the incoming terminals of the assembly under test.
  2. Assemblies protected by frequency converters where the outputs are provided with electronic short-circuit protection that limits the cut-off current with in 17 kA,
  3. Assemblies whose rated short-time withstand rating or rated conditional short-circuit current are not not more than 10 kA .
  4. Control power circuits that are fed by control transformers whose rating doesn't exceed 10kVA for a rated secondary voltage of not less than 110v or of an 1.6 kVA transformer for a rated secondary voltage less than 110 V, and whose short-circuit impedance is not less than 4 %.

 

For further information on the topic, kindly refer to clause 10.11.2 under short circuit performance.

 

Regards

S.Saravanan

Principal Technical Expert

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

MaheshReganti
Ensign MaheshReganti Ensign
Ensign

Posted: ‎2021-07-21 04:44 AM

0 Likes
0
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-21 04:44 AM

IEC 61439 standard has clearly defined 12 tests ( 7 Verification of Constructional and 5 Verification of Performance )

These 12 type tests are must to be conducted as per IEC guidelines.

Based on the successful completion of the 12 type test, the product is certified as IEC 61439 verified.

 

To specifically answer to your question on "Short circuit" withstand test,

      Yes Short circuit test is one of the 5 performance test that a LV panel to be tested.

 

Hope i have clarified your question

please feel free to reply and also do share further inputs which can enable your business and differentiate with competition technically .

 

Mahesh Reganti
Product manager - Blokset, LV switchboard
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ARJUN_SOMALA
ARJUN_SOMALA
Cadet

Posted: ‎2022-02-09 09:26 PM

In response to Anonymous user
0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-09 09:26 PM

Thanks for your informative talks regards to latest IEC 61439..

 

Needs small clarifications in respect of the following...

 

Clause 10.10.2.3.7 a) Main bus-bars shall be tested separately.

  • In this case shall the main breaker to be taken in the circuit (or) shall we have to test only on HBB alone bypassing Main breaker ?
  • The test shall be carried out at the rated current. The test current
    shall pass through the full length of the bus bars. Q:Can this current be different from rated current of the Assembly?
  • Where the design of the assembly permits, and, to minimize the influence of the external test conductors on the temperature rise,the length of the main bus bar within the enclosure for the test shall be a minimum of
    2 m and include a minimum of one joint when the bus bars are extendable.  Q: Can the main bus bar length can be less than 2m due to design constraints.

 

Could you please give your comments..

 

Regards

Arjuna

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore