Cable size for Grounding

Expert on Demand for Standards & Regulations

Widiyatmoko
Ensign
Ensign
0 Likes
3
109

Cable size for Grounding

Pak @HelvinHermanT do you have any standard for cable size for grounding cable how many % from phase/line cable size ?

Tags (1)
3 Replies 3
faisalamir
Lieutenant Lieutenant
Lieutenant

Re: Cable size for Grounding

Dear pak Moko,

 

untuk penentuan besaran gorunding cable dapat mengacu pada IEC 60364-5-54

 

Perlu didefinisikan terlebih dahulu untuk nilai prospective short circuit current (I) dan durasi masksimum short circuit tersebut (t)

Sedangkan untuk nilai koefisien "k" merujuk pada tbale B1 dibawah sesuai material konduktor yang digunakan

 

Dimana rumus yang digunakan adalah sebagai berikut:

 

Annotation 2022-04-08 112225.pngAnnotation 2022-04-08 112226.png

 

 Semoga informasi ini membantu

 

Salam,

Faisal 

Tags (1)
HelvinHermanT
Captain Captain
Captain

Re: Cable size for Grounding

Terima kasih Pak Faisalamir,

 

Sebagai tambahan infomasi Update dari IEC 60364-5-54 keluaran April 2021 sebagai berikut

 

Luas penampang konduktor harus dihitung (Ayat 543.1.2) atau dipilih sesuai dengan Tabel 54.2

Cross section.jpg

Untuk Tabel Value of k.

 

Tabel Value k.jpg

Tabel Value k 2.jpg

Tags (1)
faisalamir
Lieutenant Lieutenant
Lieutenant

Re: Cable size for Grounding

pak @HelvinHermanT 

 

Terima kasih atas tambahan informasi-nya

 

Regards,

Faisal 

Tags (1)