Bagaimana standar Panel Listrik untuk rumah sakit?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Bagaimana standar Panel Listrik untuk rumah sakit?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-11-12 08:13 AM

1 Like
2
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-12 08:13 AM

Bagaimana standar Panel Listrik untuk rumah sakit?

Halo, apakah bisa share informasi standar Panel Listrik untuk rumah sakit? Terima kasih

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-15 05:58 AM . Last Modified: ‎2021-11-15 05:59 AM

0 Likes
1
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-15 05:58 AM . Last Modified: ‎2021-11-15 05:59 AM

Hi Pak, terima kasih pertanyaannya.

 

Mengenai Standar Panel Listrik untuk rumah sakit bisa kita lihat pada IEC IEC 60364-7-710 Edition 2.0 2021-05  Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations.

 

Bisa dilihat pada ayat 7.10.51 :

 

710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electric supply system for safety services.

 

710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.


NOTE 1 The 25 m are related to possible capacitive leakage current.
Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.

 

NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location
area assigned to it and where the main power supply voltage is monitored for operating the change-over to the
electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.

 

 

Bisa disimpulkan bahwa Standar Panel Listrik untuk rumah Sakit adalah mengacu pada IEC 61439 (semua bagian) yang artinya menggunakan Panel Listrik yang memiliki uji tipe (Type Tested IEC 61439). Dalam hal ini bisa menggunakan Panel Listrik yang memiliki uji tipe dari Schneider Electric : Prisma iPM, Blokset & Okken.

 

Untuk lokasi Panel dalam radius 25 meter dari area yang di layani / di suplai dan pada lantai yang sama.

 

@FerryKurniawan 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-15 05:58 AM . Last Modified: ‎2021-11-15 05:59 AM

0 Likes
1
1163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-15 05:58 AM . Last Modified: ‎2021-11-15 05:59 AM

Hi Pak, terima kasih pertanyaannya.

 

Mengenai Standar Panel Listrik untuk rumah sakit bisa kita lihat pada IEC IEC 60364-7-710 Edition 2.0 2021-05  Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations.

 

Bisa dilihat pada ayat 7.10.51 :

 

710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electric supply system for safety services.

 

710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.


NOTE 1 The 25 m are related to possible capacitive leakage current.
Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.

 

NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location
area assigned to it and where the main power supply voltage is monitored for operating the change-over to the
electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.

 

 

Bisa disimpulkan bahwa Standar Panel Listrik untuk rumah Sakit adalah mengacu pada IEC 61439 (semua bagian) yang artinya menggunakan Panel Listrik yang memiliki uji tipe (Type Tested IEC 61439). Dalam hal ini bisa menggunakan Panel Listrik yang memiliki uji tipe dari Schneider Electric : Prisma iPM, Blokset & Okken.

 

Untuk lokasi Panel dalam radius 25 meter dari area yang di layani / di suplai dan pada lantai yang sama.

 

@FerryKurniawan 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-17 07:10 PM

In response to HelvinHermanT
1 Like
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-17 07:10 PM

Ah, baik, berarti menggunakan panel dengan standard IEC 61439 ya Pak @HelvinHermanT . Terima kasih Pak atas informasinya!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore