Posted: 2021-07-1712:15 AM
Jika polusi harmonik cukup tinggi (20% < Gh/Sn < 30%), maka harus menggunakan detuned reactor yang dirangkai seri dengan kapasitor tipe H-Duty.
Penentuan Ratingnya mengikuti besaran Capacitor per stepnya
Detuned reactor baiknya di pisah dalam ruang panel tersediri tidak tercampur dengan componen lain terutama Capacitor dikarenakan Detuned reactor menghasilkan panas.