Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Bagaimana menentukan rating Detuned Reactor dan dimana posisi untuk menempatkan Detuned Reactor dalam Capacitor Bank?
Expert on Demand for Standards & Regulations
Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-1712:15 AM
Jika polusi harmonik cukup tinggi (20% < Gh/Sn < 30%), maka harus menggunakan detuned reactor yang dirangkai seri dengan kapasitor tipe H-Duty.
Penentuan Ratingnya mengikuti besaran Capacitor per stepnya
Detuned reactor baiknya di pisah dalam ruang panel tersediri tidak tercampur dengan componen lain terutama Capacitor dikarenakan Detuned reactor menghasilkan panas.