Apakah switchgear 11 kV fixed wajib diberi earth switch? Apakah benar earth switch hanya untuk switchgear withdrawable?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Apakah switchgear 11 kV fixed wajib diberi earth switch? Apakah benar earth switch hanya untuk switchgear withdrawable?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
VickyTanzil
Ensign VickyTanzil Ensign
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-11-28 04:42 PM

0 Likes
5
1579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-28 04:42 PM

Apakah switchgear 11 kV fixed wajib diberi earth switch? Apakah benar earth switch hanya untuk switchgear withdrawable?

Pagi, mau tanya, apakah switchgear 11 kV fixed wajib diberi earth switch? Dan apakah benar earth switch hanya untuk switchgear withdrawable? Terima kasih

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
Lieutenant JG

Posted: ‎2021-11-28 04:54 PM

1 Like
4
1577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-28 04:54 PM

yang saya coba jelaskan disini adalah untuk panel MV , khusus nya Incoming dan Outgoing feeder adalah wajib di lengkapi dengan Earthing Switch (ES) IEC62271 mengatur untuk MV Switchgear 

 

pada cubicle lain seperti bus VT , coupler tidak wajib ada ES.

 

fungsi ES sebagai pengaman jadi nggak harus di withdrawable namun pada type fix juga perlu 

 

bayangkan jika ada line up 11kV sebagai substation mendapat power dari substation di upstream nya , , jika substation tersebut akan dipadamkan total maka power dari upstream perlu di padamkan , dan di lineup ini ES nya di fungsikan dan interlock sedemikian sehingga tidak bisa open close apabila ES nya sudah di fungsikan, dalam kondisi ini bila upstream tiba2 di ON kan sementara masih ada pekerjan dan belum aman maka ES akan langsung mengamankan lineup tersebut sehingga Short 3phasa pada sisi upstream sementara lineup nya aman dari gangguan , demikian gambarannya 

 

salam 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-12-01 08:45 PM

In response to Anonymous user
0 Likes
1
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-01 08:45 PM

Hi Pak,

 

Dalam IEC sih saya tidak menemukan dengan jelas kewajiban memiliki Earthing Switch pada Switchgear.

 

Akan tetapi seperti jawaban Pak Dwinanto diatas bahwa dalam dunia praktis, penggunaan Earthing Switch adalah penting sekali untuk pengamanan / safety personel dan peralatan.

 

Terutama saat akan diadakan perawatan / perbaikan yang mengakses bagian yg aktif, untuk memastikan keamanan maka harus di groundingkan dengan Earthing Switch yang tentu saja sudah di kunci dengan Silih kunci (Interlocking) yang tepat. Silih kunci tersebut juga sangat penting untuk mencegah hubung singkat akibat kesalahan operasi.

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
Lieutenant JG

Posted: ‎2021-11-28 04:54 PM

1 Like
4
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-28 04:54 PM

yang saya coba jelaskan disini adalah untuk panel MV , khusus nya Incoming dan Outgoing feeder adalah wajib di lengkapi dengan Earthing Switch (ES) IEC62271 mengatur untuk MV Switchgear 

 

pada cubicle lain seperti bus VT , coupler tidak wajib ada ES.

 

fungsi ES sebagai pengaman jadi nggak harus di withdrawable namun pada type fix juga perlu 

 

bayangkan jika ada line up 11kV sebagai substation mendapat power dari substation di upstream nya , , jika substation tersebut akan dipadamkan total maka power dari upstream perlu di padamkan , dan di lineup ini ES nya di fungsikan dan interlock sedemikian sehingga tidak bisa open close apabila ES nya sudah di fungsikan, dalam kondisi ini bila upstream tiba2 di ON kan sementara masih ada pekerjan dan belum aman maka ES akan langsung mengamankan lineup tersebut sehingga Short 3phasa pada sisi upstream sementara lineup nya aman dari gangguan , demikian gambarannya 

 

salam 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-30 05:39 AM

In response to Dwinanto_Setyadi
0 Likes
3
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-30 05:39 AM

Terima kasih Pak Dwinanto.

 

Standard IEC untuk Earthing Switch bisa ilihat pada IEC 62271-102 High-voltage switchgear and controlgear - Part 102: Alternating current disconnectors and earthing switches

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-30 06:54 PM

In response to HelvinHermanT
0 Likes
2
1560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-30 06:54 PM

Terima kasih Pak @HelvinHermanT atas replynya. Menurut IEC tersebut jadi wajib tidak ya Pak? Dan apakah benar hanya wajib untuk withdrawable? Terima kasih Pak

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-12-01 08:45 PM

In response to Anonymous user
0 Likes
1
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-01 08:45 PM

Hi Pak,

 

Dalam IEC sih saya tidak menemukan dengan jelas kewajiban memiliki Earthing Switch pada Switchgear.

 

Akan tetapi seperti jawaban Pak Dwinanto diatas bahwa dalam dunia praktis, penggunaan Earthing Switch adalah penting sekali untuk pengamanan / safety personel dan peralatan.

 

Terutama saat akan diadakan perawatan / perbaikan yang mengakses bagian yg aktif, untuk memastikan keamanan maka harus di groundingkan dengan Earthing Switch yang tentu saja sudah di kunci dengan Silih kunci (Interlocking) yang tepat. Silih kunci tersebut juga sangat penting untuk mencegah hubung singkat akibat kesalahan operasi.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-12-02 04:53 PM

In response to HelvinHermanT
0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-02 04:53 PM

Oke, baik Pak @Dwinanto_Setyadi dan Pak @HelvinHermanT , terima kasih atas infonya!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore