Apakah standar IEC untuk Busway / Busduct ?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Apakah standar IEC untuk Busway / Busduct ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-04-07 09:39 AM . Last Modified: ‎2021-04-27 06:50 AM

0 Likes
2
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-07 09:39 AM . Last Modified: ‎2021-04-27 06:50 AM

Apakah standar IEC untuk Busway / Busduct ?

 

Apakah standar IEC untuk Busway / Busduct ?

 

@Nedi

Labels
  • Labels:
  • Indonesia
  • Tags:
  • bahasa Indonesia
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-04-27 06:50 AM

0 Likes
1
2061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-27 06:50 AM

Standar IEC untuk Busway / Busduct adalah IEC 60439-2 dan IEC 61439-6.

 

IEC 60439-2 terdiri dari 14 pengujian tipe & pengujian rutin.

IEC 61349-6 terdiri dari pengujian untuk kontruksi & performa untuk keamanan dan kehandalan. Terdiri dari 25 pengujian disain dan pengujian rutin.

IEC 61439-6 adalah standar terbaru dari Standar IEC untuk Busway / Busduct.

 

Untuk menjamin performa produk, pastikan produk mengikuti standar terbaru IEC 61439-6.

 

IEC 61439-6 25  :

10.2.2 Resistance to corrosion

10.2.3.1 Thermal stability

10.2.3.2 Resistance to abnormal heat and fire due to internal electric effects

10.2.4 Resistance to ultra-violet (UV) radiation

10.2.5 Lifting

10.2.6 Mechanical impact

10.2.7 Marking

10.2.101 Ability to withstand mechanical loads

10.2.102 Thermal cycling test

10.3 Degree of protection of assembly

10.4 Clearances distances

10.4 Creepage distances

10.5.2 Effective continuity between the exposed conductive parts of the BTS & the protective circuit

10.5.3 Short-circuit withstand strength of the protective circuit

10.6 Incorporation of switching devices and components

10.7 Internal electrical circuits and connections

10.8 Terminals for external conductors

10.9.2 Power-frequency withstand voltage

10.9.3 Impulse withstand voltage

10.10 Temperature-rise limits

10.11 Short-circuit withstand strength

10.12 Electromagnetic compatibility (EMC)

10.13 Mechanical operation

10.101 Resistance to flame propagation

10.102 Fire resistance in building penetration

See Answer In Context

  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-04-27 06:50 AM

0 Likes
1
2062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-27 06:50 AM

Standar IEC untuk Busway / Busduct adalah IEC 60439-2 dan IEC 61439-6.

 

IEC 60439-2 terdiri dari 14 pengujian tipe & pengujian rutin.

IEC 61349-6 terdiri dari pengujian untuk kontruksi & performa untuk keamanan dan kehandalan. Terdiri dari 25 pengujian disain dan pengujian rutin.

IEC 61439-6 adalah standar terbaru dari Standar IEC untuk Busway / Busduct.

 

Untuk menjamin performa produk, pastikan produk mengikuti standar terbaru IEC 61439-6.

 

IEC 61439-6 25  :

10.2.2 Resistance to corrosion

10.2.3.1 Thermal stability

10.2.3.2 Resistance to abnormal heat and fire due to internal electric effects

10.2.4 Resistance to ultra-violet (UV) radiation

10.2.5 Lifting

10.2.6 Mechanical impact

10.2.7 Marking

10.2.101 Ability to withstand mechanical loads

10.2.102 Thermal cycling test

10.3 Degree of protection of assembly

10.4 Clearances distances

10.4 Creepage distances

10.5.2 Effective continuity between the exposed conductive parts of the BTS & the protective circuit

10.5.3 Short-circuit withstand strength of the protective circuit

10.6 Incorporation of switching devices and components

10.7 Internal electrical circuits and connections

10.8 Terminals for external conductors

10.9.2 Power-frequency withstand voltage

10.9.3 Impulse withstand voltage

10.10 Temperature-rise limits

10.11 Short-circuit withstand strength

10.12 Electromagnetic compatibility (EMC)

10.13 Mechanical operation

10.101 Resistance to flame propagation

10.102 Fire resistance in building penetration

  • Tags:
  • bahasa Indonesia
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-06-28 04:48 AM

In response to HelvinHermanT
0 Likes
0
1940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:48 AM

UL 857 juga merupakan salah satu standar untuk Busway (UL Standard for Safety Busways)

 

@Nedi 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.