Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.
Search in
Posted: 2021-07-12 06:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 06:30 AM
Malam, saya mau bertanya, apakah kabel NYY single core ke beban 300kw panjang 350mtr boleh di jadikan satu tray dengan kabel multicore beban 400kw panjang 300mtr? Mengingat Single core rawan unbalance impedance jika tidak ditata dengan benar. Adakah aturan yang mengatur batas panjang max pemakaian kabel single core? Terima kasih.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-13 08:59 PM
Hi Pak,
Untuk unbalance atau tidak sebenarnya karena pembagian beban yang tidak seimbang, jadi tidak ada hubungan dengan kabel single core menyebabkan unbalance. Terkadang jika beban diketahu unbalance, dipilih menggunakan kabel single core karena besaran Netral bisa di set lebih besar daripada phasanya. Bisa dilakukan simulasi dengan software ECODIAL.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 05:05 AM
ECODIAL adalah software dari Schneider Electric utk menghitung drop voltage, short cicuit, ukuran kabel, ukuran rating breaker, transformer, dll dalam bentuk SLD (single line diagram) yg bisa export dalam bentuk dokumen pdf, Software ini free dan bisa diunduh dari seamless portal utk konsultan sbb : https://www.se.com/myschneider/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-13 08:59 PM
Hi Pak,
Untuk unbalance atau tidak sebenarnya karena pembagian beban yang tidak seimbang, jadi tidak ada hubungan dengan kabel single core menyebabkan unbalance. Terkadang jika beban diketahu unbalance, dipilih menggunakan kabel single core karena besaran Netral bisa di set lebih besar daripada phasanya. Bisa dilakukan simulasi dengan software ECODIAL.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 05:05 AM
ECODIAL adalah software dari Schneider Electric utk menghitung drop voltage, short cicuit, ukuran kabel, ukuran rating breaker, transformer, dll dalam bentuk SLD (single line diagram) yg bisa export dalam bentuk dokumen pdf, Software ini free dan bisa diunduh dari seamless portal utk konsultan sbb : https://www.se.com/myschneider/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-15 08:39 PM
Ok, terima kasih infonya Pak @HelvinHermanT , Pak @Widiyatmoko
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.