Apa bedanya CAT5 dan CAT6 ya?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Apa bedanya CAT5 dan CAT6 ya?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-11-01 12:52 AM

1 Like
2
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-01 12:52 AM

Apa bedanya CAT5 dan CAT6 ya?

Siang, saya mau tanya, bedanya CAT5 dan CAT6 apa ya? Terima kasih.

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-01 06:19 PM

0 Likes
1
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-01 06:19 PM

Terima kasih pertanyaannya. Berikut informasi yang bisa saya dapatkan (lihat sumber dibawah).

 

Kabel CAT5 dan CAT6, umumnya digunakan sebagai kabel jaringan, dirancang untuk menghubungkan komputer, peralatan jaringan, dan perangkat ke modem, server, dan sakelar. Permintaan untuk bandwidth yang lebih tinggi telah meningkat selama bertahun-tahun. Akibatnya, begitu pula dengan perkembangan kabel-kabel ini. Kabel yang lebih baru telah dibawa ke industri TI dengan kemampuan yang lebih besar, seperti kinerja yang lebih tinggi dan pengurangan crosstalk.

 

Kesamaan
Membandingkan antara kabel CAT5 dan CAT6, dapat kita lihat secara visual kesamaan di antara mereka.

Mereka dibangun sama; kabel berperingkat kategori yang diakhiri dengan colokan modular RJ-45 di setiap ujungnya.

Juga colokan modular terlihat sama dengan delapan posisi konduktor berlapis emas.

Memanfaatkan steker yang sama memungkinkan mereka untuk memasukkan ke jack Ethernet yang sama pada panel patch, konektor modular, komputer, router, atau sejenisnya. Namun, perbedaan utama terletak pada bahan dan kemampuannya.

 

Ada banyak perbedaan antara kabel CAT5 dan CAT6; seperti kinerja, jenis kabel, jenis jaket dan biaya, antara lain.

 

Saat memilih mana yang akan digunakan, pertama-tama kita harus mempertimbangkan jumlah bandwidth yang harus didukung kabel. CAT5 dapat mendukung hingga 10/100 Mbps pada bandwidth 100MHz. Namun, versi terbaru dari kabel CAT5 di pasaran, CAT5e, dapat mendukung hingga 100/1000 Mbps pada bandwidth 350MHz. Sebagai perbandingan, CAT6 dapat mendukung hingga 1000 Mbps (1GbE) pada bandwidth 250MHz. Lebih baik lagi, versi CAT6 yang lebih baru yang ditawarkan Cablesys dapat mendukung hingga 1GbE pada bandwidth 500MHz.

 

Faktor utama lain yang mempengaruhi kinerja adalah jumlah lilitan yang dimiliki kabel. Sementara kabel CAT5e memiliki satu setengah hingga dua lilitan per sentimeter, kabel CAT6 lebih rapat dan memiliki dua lilitan atau lebih per sentimeter.

Aspek ketiga adalah diameter keseluruhan kabel. Aliran udara adalah pertimbangan utama di pusat data. Karena lebih banyak kabel ditambahkan ke area penambalan, itu akan membatasi aliran udara yang diperlukan untuk mendinginkan server dan peralatan. Kabel CAT6 memiliki diameter lebih tebal sekitar 0,250 inci maksimum sedangkan kabel CAT5e memiliki diameter lebih kecil sekitar 0,204 inci.

 

Akhirnya, perbedaan utama lainnya adalah biayanya. Harga bervariasi tergantung panjang dan merek. Secara umum, kabel CAT6 sekitar 10% hingga 20% lebih mahal dibandingkan dengan kabel CAT5e.

 

Sumber : https://cablesys.com/updates/differences-between-cat5-cat6-cables/

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-01 06:19 PM

0 Likes
1
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-01 06:19 PM

Terima kasih pertanyaannya. Berikut informasi yang bisa saya dapatkan (lihat sumber dibawah).

 

Kabel CAT5 dan CAT6, umumnya digunakan sebagai kabel jaringan, dirancang untuk menghubungkan komputer, peralatan jaringan, dan perangkat ke modem, server, dan sakelar. Permintaan untuk bandwidth yang lebih tinggi telah meningkat selama bertahun-tahun. Akibatnya, begitu pula dengan perkembangan kabel-kabel ini. Kabel yang lebih baru telah dibawa ke industri TI dengan kemampuan yang lebih besar, seperti kinerja yang lebih tinggi dan pengurangan crosstalk.

 

Kesamaan
Membandingkan antara kabel CAT5 dan CAT6, dapat kita lihat secara visual kesamaan di antara mereka.

Mereka dibangun sama; kabel berperingkat kategori yang diakhiri dengan colokan modular RJ-45 di setiap ujungnya.

Juga colokan modular terlihat sama dengan delapan posisi konduktor berlapis emas.

Memanfaatkan steker yang sama memungkinkan mereka untuk memasukkan ke jack Ethernet yang sama pada panel patch, konektor modular, komputer, router, atau sejenisnya. Namun, perbedaan utama terletak pada bahan dan kemampuannya.

 

Ada banyak perbedaan antara kabel CAT5 dan CAT6; seperti kinerja, jenis kabel, jenis jaket dan biaya, antara lain.

 

Saat memilih mana yang akan digunakan, pertama-tama kita harus mempertimbangkan jumlah bandwidth yang harus didukung kabel. CAT5 dapat mendukung hingga 10/100 Mbps pada bandwidth 100MHz. Namun, versi terbaru dari kabel CAT5 di pasaran, CAT5e, dapat mendukung hingga 100/1000 Mbps pada bandwidth 350MHz. Sebagai perbandingan, CAT6 dapat mendukung hingga 1000 Mbps (1GbE) pada bandwidth 250MHz. Lebih baik lagi, versi CAT6 yang lebih baru yang ditawarkan Cablesys dapat mendukung hingga 1GbE pada bandwidth 500MHz.

 

Faktor utama lain yang mempengaruhi kinerja adalah jumlah lilitan yang dimiliki kabel. Sementara kabel CAT5e memiliki satu setengah hingga dua lilitan per sentimeter, kabel CAT6 lebih rapat dan memiliki dua lilitan atau lebih per sentimeter.

Aspek ketiga adalah diameter keseluruhan kabel. Aliran udara adalah pertimbangan utama di pusat data. Karena lebih banyak kabel ditambahkan ke area penambalan, itu akan membatasi aliran udara yang diperlukan untuk mendinginkan server dan peralatan. Kabel CAT6 memiliki diameter lebih tebal sekitar 0,250 inci maksimum sedangkan kabel CAT5e memiliki diameter lebih kecil sekitar 0,204 inci.

 

Akhirnya, perbedaan utama lainnya adalah biayanya. Harga bervariasi tergantung panjang dan merek. Secara umum, kabel CAT6 sekitar 10% hingga 20% lebih mahal dibandingkan dengan kabel CAT5e.

 

Sumber : https://cablesys.com/updates/differences-between-cat5-cat6-cables/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-03 12:28 AM

In response to HelvinHermanT
1 Like
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 12:28 AM

Ah, baik, terima kasih atas informasi lengkapnya Pak @HelvinHermanT 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore