This section of the Properties dialog box, accessed by right-clicking an energy system or by clicking the relevant icon at the bottom of the energy system, provides relevant information that identifies this subsystem.
The information may vary based on the subsystem type. Lighting covers the lighting used to light the data center.
Configuration
Power path
Identifies if this subsystem is on the critical or primary power path, or if it is not included in this energy system.
Calculation source
Identifies if the load of the subsystem is measured (live) or computed (without power meters).
Actual kW Nameplate
Sums up the total nameplate value of all equipment in this subsystem.
Usable fraction of nameplate w/o derating
Identifies the usable fraction of power that can be used within the devices in this subsystem without derating the value.
Redundancy
Identifies the redundancy of this subsystem. For example, if you have a redundant setup with two 80 kW UPS, this value would be 2N.
Redundancy "+1" kW Increment
Identifies the loss in kilowatt caused by internal redundancy. (Only needed if redundancy option includes +1.)
Derate Capacity fraction
Identifies the usable fraction of the nameplate value that can be used in this subsystem. For example, if you use a 20% safety margin, this value would be 0.8.
Typical PU
Identifies the power usage (PU) of this subsystem relative to the total power usage.
Fixed loss
Identifies the fraction of power that is the fixed loss of the subsystem.
Proportional loss
Identifies the fraction of power that is lost proportional to the load of the subsystem.
Square Law loss
Identifies the fraction of power that is lost proportional to the square of the load of the subsystem.
Dry bulb fixed loss
Identifies the fraction of power that is lost per degree Celsius dry bulb.
Script
Opens the script editor for editing scripts for this subsystem.