You can access and edit the data on the property tabs defining the configuration for IT load, infiltration, ventilation, and lighting by right-clicking an energy system and selectingPropertiesor by clicking the icons at the bottom of theEnergy Systempane. The configuration options vary based on the type of subsystem.
Right-click the energy system and select> Properties> Ventilation.
Define the general settings for the energy system's ventilation.
Select if the ventilation is on the critical or primary power path, or if there is no ventilation to be included in this energy system.
Select if the ventilation data is measured (live) or computed (without power meters).
Define the configuration of the energy system's ventilation.
InActual kW Nameplate, type the total nameplate value of the ventilation.
InUsable fraction of nameplate w/o derating, type a number between 0 and 100, indicating the usable fraction of power that can be used within the devices in this subsystem without derating.
InRedundancy, type the redundancy of the subsystem.
InRedundancy +1 kW Increment, type the loss in kilowatt caused by internal redundancy. (Only needed if the redundancy option includes +1)
InDerate Capacity fraction, type a number between 0 and 1, indicating the usable fraction of the ventilation equipment nameplate value.
InTypical PU, type the power usage (PU) of the ventilation in power units relative to the total power usage.
Define the loss configuration of the energy system's ventilation.
InFixed loss, type a number between 0 and 100, indicating the fraction of power that is the fixed loss of the ventilation.
InProportional loss, type a number between 0 and 100, indicating the fraction of power that is lost proportional to the load of the data center.
InSquare Law loss, type a number between 0 and 100, indicating the fraction of power that is lost proportional to the square of the load of the data center.
InDry bulb fixed loss, type a number between 0 and 100, indicating the fraction of power lost per degree Celsius dry bulb.
Use theScripttab for writing scripts that retrieve measurements.
ClickLightingand repeat the above steps for configuring the energy system's lighting settings.