Hi!
I have a solution made in SEAL Design that I can't deploy directly to the intended server. I would like to export the solution so that I can import it to the device when I have access to it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-04 06:02 AM . Last Modified: 2024-12-04 06:03 AM
Hello, thank you for your question.
Currently there is no way to export the entire solution as it would have been deployed to a server, however, if you can connect to a device using Workstation you can also connect using SEAL! When in the same stage as you would have imported, connect using SEAL instead and deploy your solution.
If you really need the export, you’ll have to deploy to a dummy server and export using Workstation.
Lastly, you can download a few resources using the “documents” and “preview” buttons in the top right corner when in the “Applications” view.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-04 06:02 AM . Last Modified: 2024-12-04 06:03 AM
Hello, thank you for your question.
Currently there is no way to export the entire solution as it would have been deployed to a server, however, if you can connect to a device using Workstation you can also connect using SEAL! When in the same stage as you would have imported, connect using SEAL instead and deploy your solution.
If you really need the export, you’ll have to deploy to a dummy server and export using Workstation.
Lastly, you can download a few resources using the “documents” and “preview” buttons in the top right corner when in the “Applications” view.