ZS values
Hi
I'm trying to use the software but the results do not seem to show the system ZS and R1, R2 values. Is there an option to show these calculated values?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-0709:03 PM
Hi
Thanks for reaching the “EcoStruxure Power Design – Forum”
In Ecodial application, once after changing the ‘type of system earthing arrangement’ at the ‘ML/LV Transformer’ you can see the options to change resistance R1 & R2.