EcoStruxure Power Design Forum
Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-07 04:29 AM
Hello, sir.
In the end of the report it said " See the values of each feeder for the Voltage Drop and Short Circuit Calculations " but I did not see any information in this section. Could you please tell me what is the problem here? And what is the solution?
Thank you, sir.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 04:07 AM
The results shown at the feeder level; has combained...
The voltage drop of the busway (only for the distance at which the feeder is connected from the supplying point) and 'cable length of the feeder.'
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 01:41 AM
Hello,
Thanks for reaching the EcoStruxure Power Design–Forum.
Regards,
Team – Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 01:50 AM
But sir, there is cable between circuit breaker and load. If the voltage drop on the the feeder circuit is the voltage drop value of busway feeder, how about the voltage drop of that cable?
Thank you, sir.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 04:07 AM
The results shown at the feeder level; has combained...
The voltage drop of the busway (only for the distance at which the feeder is connected from the supplying point) and 'cable length of the feeder.'
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.