Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Same load with different breaker sizing result

EcoStruxure Power Design Forum

Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Power Distribution Software
  • EcoStruxure Power Design Forum
  • Same load with different breaker sizing result
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Lt. Commander Genghiz Lt. Commander
28
Karthikeyan1
Ensign Karthikeyan1 Ensign
4
Sayani_Sikdar
Ensign Sayani_Sikdar Ensign
3
ArjunSwamy
Ensign ArjunSwamy Ensign
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Power Design Forum
Solved
CVSD
Crewman CVSD
Crewman

Posted: ‎2022-08-28 06:21 PM

0 Likes
3
562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-28 06:21 PM

Same load with different breaker sizing result

Hi,

 

I am new with Ecodial and I found that this software is useful.

I am playing with the software to see breaker sizing result and I am surprise that the result is difference even with same load. Please guide me to get this? Please see red arrow attached.

Attachments
Labels
  • Labels:
  • Ecodial
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-08-29 12:32 AM . Last Modified: ‎2022-08-31 04:05 AM

In response to CVSD
0 Likes
0
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 12:32 AM . Last Modified: ‎2022-08-31 04:05 AM

Hello Ma'mun,

Thanks for your reply and for the given project file (.eac)

 

Our comments:

At the given project file there are many ‘1P+N’ load, and they are connected (Or) forced to a specific (Lx + N) line to neutral connection.

 

Suggestion:

If we make a ‘Auto’ choice for connecting these loads, then the application manages the ‘automatic load balancing’ as shown here.

Auto - Selection to distribute the loadsAuto - Selection to distribute the loads

Result : 

The outcome of this automatic load balancing, has lead to the same current at both the 'circuit breakers' (QA23 & QA35) as shown below. This has also brought same results/products as well. 

 

 

Same Sizing Current (IB) and Same SolutionSame Sizing Current (IB) and Same Solution

 

 

Thanks & regards,

Team – Ecodial Expert Support.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-08-28 09:53 PM

0 Likes
2
549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-28 09:53 PM

Hello Ma'mun,

Thanks for reaching the forum “EcoStruxure Power Design.”

 

Our comments : 

 

For the network, that you have given…

Can you please check the “Ib” used for sizing the circuit breaker? This can be verified as shown below (select the device and check the properties).

 

Checking the Ib (A)Checking the Ib (A)

 

 

This design current (Ib) will have an important impact on the sizing of ‘the protection device.’

In this situation, both the circuit breaker may have a different design current (Ib).

 

 

Feel free to comeback, if the provided explanation does not answer your query.

If any further analysis is required, then please provide the project file (.eac) created from EcoStruxure Power Design-Ecodial.

 

Thanks & regards,

Team – Ecodial Expert Support.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CVSD
Crewman CVSD
Crewman

Posted: ‎2022-08-28 11:07 PM

In response to Genghiz
0 Likes
1
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-28 11:07 PM

Hello @Genghiz,

 

Both Ib generate different values (20.6 A and 19.9 A). What reason behind this?

Please see the files attached.

Attachments
TestSoftware.zip
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-08-29 12:32 AM . Last Modified: ‎2022-08-31 04:05 AM

In response to CVSD
0 Likes
0
540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 12:32 AM . Last Modified: ‎2022-08-31 04:05 AM

Hello Ma'mun,

Thanks for your reply and for the given project file (.eac)

 

Our comments:

At the given project file there are many ‘1P+N’ load, and they are connected (Or) forced to a specific (Lx + N) line to neutral connection.

 

Suggestion:

If we make a ‘Auto’ choice for connecting these loads, then the application manages the ‘automatic load balancing’ as shown here.

Auto - Selection to distribute the loadsAuto - Selection to distribute the loads

Result : 

The outcome of this automatic load balancing, has lead to the same current at both the 'circuit breakers' (QA23 & QA35) as shown below. This has also brought same results/products as well. 

 

 

Same Sizing Current (IB) and Same SolutionSame Sizing Current (IB) and Same Solution

 

 

Thanks & regards,

Team – Ecodial Expert Support.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc