Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-28 06:21 PM . Last Modified: 2024-11-22 04:25 AM
Hi,
I am new with Ecodial and I found that this software is useful.
I am playing with the software to see breaker sizing result and I am surprise that the result is difference even with same load. Please guide me to get this? Please see red arrow attached.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-29 12:32 AM . Last Modified: 2022-08-31 04:05 AM
Hello Ma'mun,
Thanks for your reply and for the given project file (.eac)
Our comments:
At the given project file there are many ‘1P+N’ load, and they are connected (Or) forced to a specific (Lx + N) line to neutral connection.
Suggestion:
If we make a ‘Auto’ choice for connecting these loads, then the application manages the ‘automatic load balancing’ as shown here.
Result :
The outcome of this automatic load balancing, has lead to the same current at both the 'circuit breakers' (QA23 & QA35) as shown below. This has also brought same results/products as well.
Thanks & regards,
Team – Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-28 09:53 PM
Hello Ma'mun,
Thanks for reaching the forum “EcoStruxure Power Design.”
Our comments :
For the network, that you have given…
Can you please check the “Ib” used for sizing the circuit breaker? This can be verified as shown below (select the device and check the properties).
This design current (Ib) will have an important impact on the sizing of ‘the protection device.’
In this situation, both the circuit breaker may have a different design current (Ib).
Feel free to comeback, if the provided explanation does not answer your query.
If any further analysis is required, then please provide the project file (.eac) created from EcoStruxure Power Design-Ecodial.
Thanks & regards,
Team – Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-29 12:32 AM . Last Modified: 2022-08-31 04:05 AM
Hello Ma'mun,
Thanks for your reply and for the given project file (.eac)
Our comments:
At the given project file there are many ‘1P+N’ load, and they are connected (Or) forced to a specific (Lx + N) line to neutral connection.
Suggestion:
If we make a ‘Auto’ choice for connecting these loads, then the application manages the ‘automatic load balancing’ as shown here.
Result :
The outcome of this automatic load balancing, has lead to the same current at both the 'circuit breakers' (QA23 & QA35) as shown below. This has also brought same results/products as well.
Thanks & regards,
Team – Ecodial Expert Support.