Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

IEC 60364-5-52 cable carrying capacity

EcoStruxure Power Design Forum

Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Power Distribution Software
  • EcoStruxure Power Design Forum
  • IEC 60364-5-52 cable carrying capacity
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Lt. Commander Genghiz Lt. Commander
28
Karthikeyan1
Ensign Karthikeyan1 Ensign
4
Sayani_Sikdar
Ensign Sayani_Sikdar Ensign
3
ArjunSwamy
Ensign ArjunSwamy Ensign
1
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Power Design Forum
Solved
KrunoslavSever
Crewman KrunoslavSever Crewman
Crewman

Posted: ‎2022-12-16 06:19 AM

0 Likes
4
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-16 06:19 AM

IEC 60364-5-52 cable carrying capacity

EcoStruxure power design - Ecodial 4.9.8 & Ecostruxure power design E1.94

Hi,

I've noticed that current carrying capacities or Iz are not aligned with table B.52.10 in my calculations. My case is with installation method 31 / E or multicore cables on horizontal perforated tray for PVC type cables made of copper. Temperature for ambiental air is set to 30°, and I'm looking at one cable per tray. Ecodial gives me for 10 mm2=54.5A, for 16 mm2=72,7A, for 25 mm2=91,8A, and so on. From IEC 60364-5-52 table B.52.10 currents should be 60, 80 and 101 amps for those mentioned cables. Is there some factor that I'm missing?

In the other software Ecostruxure power design, I'm getting capacities according to mentioned table.

Thank you.

 

Best regards

Kruno

Labels
  • Labels:
  • Ecodial
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-12-19 11:58 PM

In response to KrunoslavSever
0 Likes
1
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 11:58 PM

Hello

Thanks for the given project file.

At the given example, the circuit protection is considered as “FUSE.”

In this case, there is an additional coefficient is considered based on the type of protective device.

Coefficient with respect to protection deviceCoefficient with respect to protection device

As compared to my example; here the value (60 Amps) is multiplied by 1.10 and resuled to 54.5 =~ 55 

We confirm; that the application is working as expected.

 

Regards,

Team - Ecodial Expert Support

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-12-19 03:24 AM . Last Modified: ‎2022-12-19 03:30 AM

0 Likes
0
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 03:24 AM . Last Modified: ‎2022-12-19 03:30 AM

 

Hello

Thanks for your interest in Ecodial.

In the following image: we can see the results from the Ecodial for the ‘load of 50 Amps’ with inputs defined by the user.

 

Installation method 31 / E

Multicore cables

On horizontal perforated tray f

Insulation: PVC type cables

Material: copper.

Air ambient temperature: 30°

Arrangement: one cable per tray.

 

Ecodial Result.png

 

In our analysis; the results are coming as expected.

If you need further analysis, then kindly please share with us the project file.

 

Regards, 

Team-Ecodial Expert Support.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Crewman KrunoslavSever Crewman
Crewman

Posted: ‎2022-12-19 04:09 AM

0 Likes
2
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 04:09 AM

Many thank's for your reply Genghiz,

you can find the file in attachment. I'm still getting smaller currents. For example, cable cross section of 10 mm2 returns 54.5 amps.

Attachments
compare.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Lt. Commander Genghiz Lt. Commander
Lt. Commander

Posted: ‎2022-12-19 11:58 PM

In response to KrunoslavSever
0 Likes
1
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 11:58 PM

Hello

Thanks for the given project file.

At the given example, the circuit protection is considered as “FUSE.”

In this case, there is an additional coefficient is considered based on the type of protective device.

Coefficient with respect to protection deviceCoefficient with respect to protection device

As compared to my example; here the value (60 Amps) is multiplied by 1.10 and resuled to 54.5 =~ 55 

We confirm; that the application is working as expected.

 

Regards,

Team - Ecodial Expert Support

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Crewman KrunoslavSever Crewman
Crewman

Posted: ‎2022-12-20 12:39 AM

In response to Genghiz
0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-20 12:39 AM

Thank you for reply. 

In the other software Ecostruxure power design, values are the same in case of a fuse or a circuit breaker (that is contrary).

Thank you again for ecodial analysis.

Best regards

Kruno

Attachments
comparison.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc