How to create a totally selective network?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • How to create a totally selective network?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-10-26 11:59 PM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
3
3345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-26 11:59 PM . Last Modified: ‎2024-11-22 04:25 AM

How to create a totally selective network?

I need to create a totally selective network for my client. I am exploring to see how I can use Ecodial to achieve this. Sometimes I get some errors and I can only get limited selectivity. Are there any specific ways to work on this?

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-10-27 12:25 AM . Last Modified: ‎2020-12-02 03:59 AM

0 Likes
1
3340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 12:25 AM . Last Modified: ‎2020-12-02 03:59 AM

Thanks for your query on achieving the 'Total Selectivity' in your network design. The following comments would help you in understanding the same.

 

Principles of Selectivity

 

Selectivity is achieved by overcurrent and earth fault protective devices.

If a fault condition, occurring at any point in the installation, is cleared by the protective device located immediately upstream of the fault, while all other protective devices remain unaffected.

 

Applications

 

  • Selectivity is required for installation supplying critical loads where one fault on one circuit shall not cause the interruption of the supply of other circuits.
  • In IEC 60364 series it is mandatory for installation supplying safety services and in some special applications like
    • Medical
    • Marine
    • High-rise building
    • Data centers
    • Infrastructure (Tunnel, Airport…)
    • Critical process

 

How to achieve the Selectivity

 

  • From installation point of view, Selectivity is achieved when the maximum short-circuit current at a point of installation is below selectivity limit of the circuit breakers supplying this point of installation.
  • Selectivity shall be checked for all circuits supplied by one source and for all type of fault:
    • Overload
    • Short-circuit
    • Earth fault
  • When system can be supplied by different sources (Grid or generator set for instance) selectivity shall be checked in both cases.
  • Selectivity between two circuit breakers may be…
    • Total     : Up to the breaking capacity of the downstream circuit breaker.
    • Partial   : Up to a specified value according to circuit breakers characteristics.
  • Different solution is provided to achieve selectivity based on…
    • Current
    • Time
    • Energy
    • Logic

Selectivity verifications at Ecodial :

 

  • The electrical network design in Ecodial, will check the "selectivity" between the two protective devices by default.
  • This supported by the backend data, defined from the "complementary technical guide."

Verification of the Selectivity at EcodialVerification of the Selectivity at Ecodial

 

  • Once after completing the network calculation, this can be verified by "selecting the protection device" and launch the "Curve" section.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-10-27 12:25 AM . Last Modified: ‎2020-12-02 03:59 AM

0 Likes
1
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 12:25 AM . Last Modified: ‎2020-12-02 03:59 AM

Thanks for your query on achieving the 'Total Selectivity' in your network design. The following comments would help you in understanding the same.

 

Principles of Selectivity

 

Selectivity is achieved by overcurrent and earth fault protective devices.

If a fault condition, occurring at any point in the installation, is cleared by the protective device located immediately upstream of the fault, while all other protective devices remain unaffected.

 

Applications

 

  • Selectivity is required for installation supplying critical loads where one fault on one circuit shall not cause the interruption of the supply of other circuits.
  • In IEC 60364 series it is mandatory for installation supplying safety services and in some special applications like
    • Medical
    • Marine
    • High-rise building
    • Data centers
    • Infrastructure (Tunnel, Airport…)
    • Critical process

 

How to achieve the Selectivity

 

  • From installation point of view, Selectivity is achieved when the maximum short-circuit current at a point of installation is below selectivity limit of the circuit breakers supplying this point of installation.
  • Selectivity shall be checked for all circuits supplied by one source and for all type of fault:
    • Overload
    • Short-circuit
    • Earth fault
  • When system can be supplied by different sources (Grid or generator set for instance) selectivity shall be checked in both cases.
  • Selectivity between two circuit breakers may be…
    • Total     : Up to the breaking capacity of the downstream circuit breaker.
    • Partial   : Up to a specified value according to circuit breakers characteristics.
  • Different solution is provided to achieve selectivity based on…
    • Current
    • Time
    • Energy
    • Logic

Selectivity verifications at Ecodial :

 

  • The electrical network design in Ecodial, will check the "selectivity" between the two protective devices by default.
  • This supported by the backend data, defined from the "complementary technical guide."

Verification of the Selectivity at EcodialVerification of the Selectivity at Ecodial

 

  • Once after completing the network calculation, this can be verified by "selecting the protection device" and launch the "Curve" section.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-10-27 12:40 AM . Last Modified: ‎2025-08-12 05:15 AM

0 Likes
0
3338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-27 12:40 AM . Last Modified: ‎2025-08-12 05:15 AM

Further detailed information you can see a similar discussion under the "Power Foundations Forum" as well.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-10-28 10:47 PM . Last Modified: ‎2020-12-02 02:07 AM

In response to Genghiz
0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-28 10:47 PM . Last Modified: ‎2020-12-02 02:07 AM

Thank you for your answer. Helped me understand this subject in detail.

 

Cheers,

Chris

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.