attaching more than 1 racks ATS to a rack PDU

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • attaching more than 1 racks ATS to a rack PDU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
OT
OT
Cadet

Posted: ‎2020-05-18 10:50 PM

0 Likes
2
1682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-18 10:50 PM

attaching more than 1 racks ATS to a rack PDU

Recently I attached 14 server with a single power supply to 2 rack ATSes (AP4423) as each one can connect only 8 servers

If I configure the power dependency, I can only configure 1 of the 2 ATSes in the Power dependencies on the 4423.

Configuring the second ATS will display the message "Rack PDU is already supplying rack ATS".

 

In order to get the power distribution correct, I connect one ATS to FEED A to as primary Connection and the other with FEED B as primary Connection. Then the single powered servers starts to complain that I there is no distributed redundancy because there no Secondary Connection..

 

How can we attach 2 rack ATSes on the same Rack PDU pair (FEED A and FEED B) in the same rack.

 

 

 

 

 

 

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2020-05-19 01:01 AM . Last Modified: ‎2020-05-28 05:39 AM

0 Likes
1
1678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-19 01:01 AM . Last Modified: ‎2020-05-28 05:39 AM

Hi Onno,

It is by design only one rack ATS can be connected to a pair of rack pdu's in a rack. It is mainly because of the predicted power and power sold estimated load strategies - they treat primary and secondary rack pdu's as if they were paired. One rack pdu cannot be paired multiple times.

Suggested workaround: Model one ATS with the combined sum of the outlets of all the other ATSs. Connect this ATS to the rack PDUs and the server equipment to the ATS.
Add the other ATSs as "dummy" ATSs, that is without connecting any equipment to them. This way the inventory reports will be valid.

Kind regards

Reply

Link copied. Please paste this link to share this article on your social media post.

OT
OT
Cadet

Posted: ‎2020-05-25 12:01 AM

In response to Jef
0 Likes
0
1660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-25 12:01 AM

This is exactly my point.

By using 2 ATS devices, one using feed A and the other FEED B you can distribute the power over the 2 rack PDUs in a redudant situation. The load on the Rack PDUs  is determinated by the power that  is connected to the ATS not how many ATS there are connected.In the end you can not put not put more power in a Rack that a single RackPDU can handle.

By limiting the all the ATS connections to only 1 ATS per RackPDU the power reservation is uneqal in a redunatant situation,

 

The Limitation of 1 ATS the RackPDU pair seems to be strange  and serves no purpus.

 

Greetings,

 

Onno.

 

 

 

 

 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore