Scheduling Device Discoveries for all Devices

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Scheduling Device Discoveries for all Devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Barliman_apc_customer
Ensign Barliman_apc_customer
Ensign

Posted: ‎2024-01-09 11:01 AM

1 Like
3
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-09 11:01 AM

Scheduling Device Discoveries for all Devices

DCE v8.0.0.149 and v 8.1.0.263

I've spent a lot of time looking but can't find how to edit discovery settings for all devices our install is monitoring. I can see how to do them individually, but not how to change them all at once.

We're monitoring about 3800 UPS's and I'd really rather not have to do them one at a time.

Anyone have the steps I need to perform to do it?

 

Regards,

Tom

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JohnBT
Lieutenant JG JohnBT Lieutenant JG
Lieutenant JG

Posted: ‎2024-01-09 05:28 PM

1 Like
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-09 05:28 PM

Hello,

 

If the Saved Discoveries tab is not present in the Monitoring perspective of the DCE Desktop Client, go to Window > Device > Click on Saved Discoveries.  This will open the Saved Discoveries tab.  Select the discovery you want to edit and it will open a window.  You can then click Next on this window until you get to the Discovery Scheduling option. 

 

Hope this helps.

 

John

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
JohnBT
Lieutenant JG JohnBT Lieutenant JG
Lieutenant JG

Posted: ‎2024-01-09 05:28 PM

1 Like
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-09 05:28 PM

Hello,

 

If the Saved Discoveries tab is not present in the Monitoring perspective of the DCE Desktop Client, go to Window > Device > Click on Saved Discoveries.  This will open the Saved Discoveries tab.  Select the discovery you want to edit and it will open a window.  You can then click Next on this window until you get to the Discovery Scheduling option. 

 

Hope this helps.

 

John

Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2024-01-10 04:41 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-10 04:41 AM

Just to confirm, you're trying to change the snmp communication settings (community strings) that were used when the device was initially discovered?  If so, thats under device-->snmp device communication settings--> device scan settings.  Then select one or more devices and edit the community strings or snmpv3 settings.

You would only need to edit the saved discoveries if you wanted to discover new devices, not existing

Reply

Link copied. Please paste this link to share this article on your social media post.

Barliman_apc_customer
Ensign Barliman_apc_customer
Ensign

Posted: ‎2024-01-16 12:41 PM

0 Likes
0
1226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 12:41 PM

What I want to do is set Discovery scheduling for all devices at once.

Right now I don't have scheduling set.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore