Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Posted: 2022-06-20 08:05 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-20 08:05 PM
I have two Netbotz 200's, netbotz1 and netbotz2. Both were running AOS 3.5.9 and App 3.5.6:
American Power Conversion Network Management Card AOS v3.5.9
(c) Copyright 2008 All Rights Reserved NetBotz 200 App v3.5.6
An ftp to both showed the following:
--wx-wx-wx 1 apc apc 1572864 May 23 2008 apc_hw03_aos_359.bin
drwxrwxrwx 1 apc apc 0 May 23 2008 sec/
--wx-wx-wx 1 apc apc 2031616 Apr 01 2009 apc_hw03_nb200_356.bin
-r--r--r-- 1 apc apc 54999 Jun 20 2022 event.txt
-r--r--r-- 1 apc apc 416 Jun 20 2022 data.txt
-rw-rw-rw- 1 apc apc 26117 Jun 20 2022 config.ini
I followed the instructions on page 104 of the User's Guide to use scp to copy over apc_hw03_aos_390.bin and then apc_hw03_nb200_375.bin. This worked fine to upgrade netbotz2:
American Power Conversion Network Management Card AOS v3.9.0
(c) Copyright 2009 All Rights Reserved NetBotz 200 App v3.7.5--wx-wx-wx 1 apc apc 1572864 May 11 2015 apc_hw03_aos_390.bin
drwxrwxrwx 1 apc apc 0 May 11 2015 sec/
--wx-wx-wx 1 apc apc 2031616 Dec 05 2012 apc_hw03_nb200_375.bin
-r--r--r-- 1 apc apc 35545 Jun 20 2022 event.txt
-r--r--r-- 1 apc apc 45226 Jun 20 2022 data.txt
-rw-rw-rw- 1 apc apc 27123 Jun 20 2022 config.ini
However, when I performed a similar scp on netbotz1, I now see:
American Power Conversion Network Management Card AOS v3.5.9
(c) Copyright 2008 All Rights Reserved NetBotz 200 App v3.7.5--wx-wx-wx 1 apc apc 1572864 May 23 2008 apc_hw03_aos_359.bin
drwxrwxrwx 1 apc apc 0 May 23 2008 sec/
When I ssh/telnet into netbotz1, "1- Device Manager" takes me to the Device Manager screen with no devices displayed.
------- Device Manager --------------------------------------------------------
<ESC>- Back, <ENTER>- Refresh
How do I fix the upgrade of this Netbotz? I have tried scp'ing over apc_hw03_aos_390.bin and apc_hw03_nb200_375.bin multiple times to no avail.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-21 04:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-21 04:50 AM
I used ftp to transfer the files to netbotz1 and that fixed the issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.