PDU firmware update unsuccessful

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • PDU firmware update unsuccessful
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-01-05 11:20 PM

0 Likes
4
3647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 11:20 PM

PDU firmware update unsuccessful

Hello,

I am trying to do a firmware update to all my PDU's via DCE server.

9 out of m 152 PDU's were unsuccessful.

I get an "unable to connect" error although those PDU's are online and responding to PING.

PDU type is AP8886

The new firmware version is  6.9.6

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-01-06 12:53 AM . Last Modified: ‎2021-01-06 12:53 AM

0 Likes
3
3635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 12:53 AM . Last Modified: ‎2021-01-06 12:53 AM

First you need to log in to the device via SSH or Serial and enable FTP using this command:

ftp -S enable

 

Next you need to download the files listed below from this link:

https://schneider-electric.box.com/s/v94kqtqgsb151rxljm47lp4bn5ajd89c

 

Connect to the NMC using FTP, I recommend the WinSCP client,

Upload "apc_hw05_bootmon_109.bin" to the root,

The NMC will reboot,

Reconnect via FTP,

Upload "apc_hw05_aos_696.bin" to the root,

The NMC will reboot,

Reconnect via FTP,

Upload "apc_hw05_rpdu2g_694.bin" to the root,

The NMC will reboot for the final time

 

-Gavan

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-01-06 12:53 AM . Last Modified: ‎2021-01-06 12:53 AM

0 Likes
3
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 12:53 AM . Last Modified: ‎2021-01-06 12:53 AM

First you need to log in to the device via SSH or Serial and enable FTP using this command:

ftp -S enable

 

Next you need to download the files listed below from this link:

https://schneider-electric.box.com/s/v94kqtqgsb151rxljm47lp4bn5ajd89c

 

Connect to the NMC using FTP, I recommend the WinSCP client,

Upload "apc_hw05_bootmon_109.bin" to the root,

The NMC will reboot,

Reconnect via FTP,

Upload "apc_hw05_aos_696.bin" to the root,

The NMC will reboot,

Reconnect via FTP,

Upload "apc_hw05_rpdu2g_694.bin" to the root,

The NMC will reboot for the final time

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-06 01:12 AM

In response to Anonymous user
0 Likes
0
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 01:12 AM

Thanks!

I have enabled the FTP server and it's working now.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-02-07 10:16 AM

In response to Anonymous user
0 Likes
1
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-07 10:16 AM

I'm trying this method via WinSCP, but the boot.bin file will not copy over to the nmc via FTP. It starts to copy and then the screen just disappears. I successfully connected via FTP. The NMC also shows that the AOS.bin file is already on there, but I am unable to delete that file. These latest updates are causing more trouble than anything. I have 334 APCs to update so one by one is not an option.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-02-08 12:35 AM

In response to Anonymous user
0 Likes
0
3515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-08 12:35 AM

Hi Willyhill,

 

These steps are only required if you are recovering from a failed update, otherwise you can still use DCE to do a bulk updated.

 

Also if you ready the steps above you will see that it will disconnect after you transfer each file and you don't delete anything.

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore