Hello,
unable to add netbotz 250 to DCE system.
when I add it as Netbotz type the system does not add it.
if I add it through SNMPV1 I have no problems.
If I add it as a Netbotz device, it does not register
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-20 11:40 PM
Hello,
The Netbotz 250 is an NMC-based device. When you discover a Netbotz 250 in DCE, it should be discovered using SNMPv1 or v3 just like any APC Network Management Cards.
The only Netbotz devices that you need to discover as a Netbotz Appliance are the Netbotz v3 appliance. (NBRK0570, NBWL0455A, NBWL0355A, etc)
Hope this helps.
Thanks,
John
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-20 11:40 PM
Hello,
The Netbotz 250 is an NMC-based device. When you discover a Netbotz 250 in DCE, it should be discovered using SNMPv1 or v3 just like any APC Network Management Cards.
The only Netbotz devices that you need to discover as a Netbotz Appliance are the Netbotz v3 appliance. (NBRK0570, NBWL0455A, NBWL0355A, etc)
Hope this helps.
Thanks,
John
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.