Posted: 2025-04-10 10:56 PM
Hi everyone,
I would like to create a p15 file with the NMC Security Wizard 1.0.1, but I get the following error.
"Unhandled exception: cryptlib.CryptException: -3: Bad argument, parameter 3
at NMCSecurityWizardCLI.Program.ImportSignedCSR(String sCertFile, String sKeyFile, String sOutFile)
at NMCSecurityWizardCLI.Program.Main(String[] args)"
Now I have read in the forum that the error only occurs with version 1.0.1. In version 1.0.0 this should work, as our command is entered correctly.
"NMCSecurityWizardCLI --import -o XXYY -s XXX.cer -p XXX"
Can you please help me with this?
Best regards
Timo
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-12 01:53 AM
Hello,
Some users may experience errors using version v1.0.1 of the CLI Security Wizard with the environment CLI Secwiz v1.0.1, I had Attached the first release version of the CLI Security Wizard, v1.0.0. Users getting error messages when importing a signed certificate, can you try to use the v1.0.0 version and see if the errors persist
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-12 01:53 AM
Hello,
Some users may experience errors using version v1.0.1 of the CLI Security Wizard with the environment CLI Secwiz v1.0.1, I had Attached the first release version of the CLI Security Wizard, v1.0.0. Users getting error messages when importing a signed certificate, can you try to use the v1.0.0 version and see if the errors persist
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of