NB750 and DCE 7.8 error Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NB750 and DCE 7.8 error Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
masolans
Ensign masolans
Ensign

Posted: ‎2020-08-04 03:28 AM

1 Like
6
4981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 03:28 AM

NB750 and DCE 7.8 error Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed

My DCE (ver 7.8) detect my new nb750 ( ver 5.2.2.63) but receive that error Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed

 

Credentials are correct, ports are open in the network

 

How can solve it?

  • Tags:
  • Data Center Expert
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TechieBala
Lieutenant JG TechieBala Lieutenant JG
Lieutenant JG

Posted: ‎2020-08-26 03:00 AM . Last Modified: ‎2020-08-26 03:12 AM

1 Like
5
4930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-26 03:00 AM . Last Modified: ‎2020-08-26 03:12 AM

Dear @masolans 

 

I have seen this error occurs for the two reasons mainly:

 

Using Netbotz 750 superuser account password instead of appliance's root account password in Device File Transfer Settings

Using the wrong protocol ie., FTP instead of SCP

 

DDF.JPG

 

DDF1.png

 

Please also refer this k-base docs that can be useful for this DDF error. 

https://www.se.com/us/en/faqs/FA381605/

https://www.apc.com/au/en/faqs/FA177004/

 

If possible, please verify these settings again and re-discover the Netbotz 750 appliance in DCE. Please also make sure that you are able to ping the Netbotz appliance IP address through DCE web UI --Status--Additional Information--Troubleshoot network--Ping. If this fails and if DCE can not ping the device, I recommend allowing ping on the device / network where applicable and see if it helps. 

 

I hope this helps. 

 

Regards,

Bala

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
TechieBala
Lieutenant JG TechieBala Lieutenant JG
Lieutenant JG

Posted: ‎2020-08-26 03:00 AM . Last Modified: ‎2020-08-26 03:12 AM

1 Like
5
4931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-26 03:00 AM . Last Modified: ‎2020-08-26 03:12 AM

Dear @masolans 

 

I have seen this error occurs for the two reasons mainly:

 

Using Netbotz 750 superuser account password instead of appliance's root account password in Device File Transfer Settings

Using the wrong protocol ie., FTP instead of SCP

 

DDF.JPG

 

DDF1.png

 

Please also refer this k-base docs that can be useful for this DDF error. 

https://www.se.com/us/en/faqs/FA381605/

https://www.apc.com/au/en/faqs/FA177004/

 

If possible, please verify these settings again and re-discover the Netbotz 750 appliance in DCE. Please also make sure that you are able to ping the Netbotz appliance IP address through DCE web UI --Status--Additional Information--Troubleshoot network--Ping. If this fails and if DCE can not ping the device, I recommend allowing ping on the device / network where applicable and see if it helps. 

 

I hope this helps. 

 

Regards,

Bala

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-03 03:36 AM

In response to TechieBala
0 Likes
4
4744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-03 03:36 AM

@TechieBala  Thanks for the information, 


I am also facing the same problem, as mentioned in the @masolans  statement, 

I have done the changes Root, and SCP settings etc. as per your reply but there is still the error persist,


I also upload the Updated DDF files from the https://ddf.ecostruxureit.com/

 

Screenshot_40.png

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

shemil_usman
Ensign shemil_usman
Ensign

Posted: ‎2020-11-03 03:54 AM

In response to Anonymous user
0 Likes
0
4737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-03 03:54 AM

@Anonymous user 

 

please try to ping from DCE Server to Netbotz750 IP.

 

If its not pinging enable/allow "icmp" in your firewall from DCE Server IP to Netbotz750 IP. 

 

Hope this helps.

 

Thanks

 

Shemil 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TechieBala
Lieutenant JG TechieBala Lieutenant JG
Lieutenant JG

Posted: ‎2020-11-03 05:13 AM

In response to Anonymous user
0 Likes
2
4731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-03 05:13 AM

Hi @Anonymous user May I know the firmware version of Netbotz 750? Is it 5.2.2 or 5.2.3? Are you trying to discover it first time on DCE? 

 

Note: The DDF file that you downloaded is different from scanner DDF. DDF needs to download the scanner DDF file from the device during the discovery process. If it fails, then DCE shows this error. 

If the issue still persists, then I suggest you to contact your regional CCC technical support team as they can guide you to resolve this issue. 

You can find the contacts in the below link:

https://www.apc.com/us/en/country-selector?ref_url=/in/en/support/contact-us/

 

Regards,

Bala

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

martinwall
Crewman martinwall
Crewman

Posted: ‎2021-01-18 07:10 AM

In response to TechieBala
0 Likes
1
4464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-18 07:10 AM

Hi, 

 

We are also having this problem brand new DCE running 7.8.0 and brand new Netbotz 750 running 5.2.2. Is 5.2.3 available? If so where can I download it from?

 

We are on a private open network with no firewall and have added root credentials to the Device File Transfer Settings, under SCP only, and superuser login details under the Netbotz Appliance credentials

 

I have added numerous 750's to DCE's before with no problem. Is it something in the firmware? 

 

Let me know

 

Kind Regards

 

Martin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-19 02:03 AM

In response to martinwall
0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-19 02:03 AM

Netbotz 5.2.4 can be downloaded here:

 

https://www.se.com/uk/en/download/document/APC_SFNBZ_524_EN/

 

DCE 7.8.1 has also been released, contact your local support team for the link.

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore