Managing door sensors/alerts for Netbotz 250 device via SNMPv3

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Managing door sensors/alerts for Netbotz 250 device via SNMPv3
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
4jp
Ensign 4jp
Ensign

Posted: ‎2024-07-01 08:45 AM

0 Likes
4
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-01 08:45 AM

Managing door sensors/alerts for Netbotz 250 device via SNMPv3

We are running DCE 7.8.1 and have a couple hundred NB 250 devices installed.

I do not know if they all have door sensors connected to them, nor do I know if they are consistently plugged into the same physical ports.

 

I want to disable all door sensor related alerts or the sensors themselves en-masse (we don't use them at all).

 

If I discover the devices in the APC SNMP Configuration menu, I see the environmental sensors but no door sensors. Why is this? Do I need to use a newer version of DCE or maybe a different DDF?

 

IS there a better way for me to do this?

 

4jp_0-1719848294664.png

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-07-02 08:13 AM

1 Like
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 08:13 AM

Hello @4jp,


Unfortunately I am unable to see your uploaded image, but below is some details around alerting for this.

Alerts within Data Center Expert and from the NetBotz itself for the dry contacts should fall into the "state" sensors category if Universal Sensor ports are being used:

Cory_McDonald_5-1719931536380.png

 

Cory_McDonald_6-1719931556087.png

 

This category of alerts also is comprised of other types of "state" sensors: fluid detector, dry contact, smoke, etc.  Due to other types of sensors being in this category, you likely can't just disable the alerts on the DCE side.

 

From my experience in topics around this, you would need to go into the NetBotz appliances web interfaces and disable "alarm generation" for the specific sensors or disconnect the sensors and then clear the lost communication of the sensor if you do not want the alerts occurring.

 

I can not see a way to be able to mass configure the alerts through DCE or using the NMC mass config utility unless you know which ports the sensors are in that you want to enable alarm generation for and which ports you want to disable alarm generation. 

 

If you know which ports to enable and disable alarm generation for, then you can use APC SNMP Device Configuration option within DCE to do the mass config:

Cory_McDonald_1-1719932740292.png

 

Unfortunately it sounds like your best option is to log into each unit and check for the sensors or physically remove the sensors from the appliances that you don't need them in and then clear the unplugged sensors alarm from the devices web interface.

Cory_McDonald_3-1719933023409.png

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

4jp
Ensign 4jp
Ensign

Posted: ‎2024-07-02 12:53 PM

0 Likes
1
632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 12:53 PM

I may have a very janky solution to this, and it involves editing the alert/event actions for each event in the environmental details tab. However I don't know how to interpret these values under the SNMP configuration section.

 

For example  NB: High Temperature Threshold Violation.[0x2E08] (Warning) has a value of ES,E[:::],T[:::::] in the SNMP config window. Is there a breakdown anywhere of how to manually edit these values or an explaination of what they mean?

Screenshot 2024-07-02 155004.jpg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Damien
Damien
Cadet

Posted: ‎2025-04-30 05:48 AM

1 Like
0
133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-30 05:48 AM

You do not have to log into each device and make this change. You can create a template in DCE from a single device after that change has been made and then configure the rest off of that change.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2025-05-01 05:56 AM

In response to 4jp
0 Likes
0
129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-01 05:56 AM

Event config syntax can be found in the following FAQ: https://www.apc.com/us/en/faqs/FA156188/

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of