Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Introducing the Constant-Density Ideal Gas Law Buoyancy Model

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Introducing the Constant-Density Ideal Gas Law Buoyancy Model
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All
Related Products
product field
Schneider Electric
EcoStruxure IT Design CFD

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
jvangilder
Ensign jvangilder Ensign
Ensign

Posted: ‎2022-05-05 05:02 AM . Last Modified: ‎2025-04-02 11:30 PM

0 Likes
1
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-05 05:02 AM . Last Modified: ‎2025-04-02 11:30 PM

Introducing the Constant-Density Ideal Gas Law Buoyancy Model

Here is post for those interested in some details of our underlying CFD technology... Recall that warm air rises and cold air sinks. We call this buoyancy. Well, we have to model that physics in ITA CFD. In fact, we just changed the buoyancy model in ITA CFD from a traditional Boussinesq approximation which uses a fluid property called the bulk thermal expansivity to what we are calling a constant-density ideal gas law model. We still assume that the air density is constant except in the buoyancy term in the vertical-direction momentum equation; for the latter term, we compute density variations due to temperature changes from the ideal gas law. As you may know, air conveniently behaves as an ideal gas in most conditions.

 

Our testing has shown negligible differences in accuracy for most practical applications - and no obvious impact on solution robustness. So why did we make the change? Two reasons: 1) We eliminated the need for the bulk thermal expansivity fluid property - simpler is better! 2) The new model is, at least, theoretically more accurate; this may be noticeable in scenarios with large temperature differences and strong buoyancy forces.

Labels
  • Labels:
  • IT Design CFD
  • Tags:
  • Buoyancy
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-04-21 04:48 AM . Last Modified: ‎2025-04-21 04:51 AM

0 Likes
0
524
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-21 04:48 AM . Last Modified: ‎2025-04-21 04:51 AM

More about EcoStruxure IT Design CFD is coming soon in the EcoStruxure IT Help Center.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore