Hello,
I am looking for a genome for the "Amphenol Network Solutions" team, I was looking for one within the genomes but was unsuccessful, is there anyone who can help?
Amphenol Network Solutions > 60A DUAL-FEED COMPACT GMT FUSE PANEL (amphenol-ns.com)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-14 05:52 AM . Last Modified: 2022-09-14 05:53 AM
Hi Martin,
If I understand correctly you want to power your asset from a rack-ats and also from another source (rack pdu /rack ats), right? if yes, then that is not supported.
When we connect a rack mounted item/server with 2N redundancy, then it may/can be connected to 2 different power supplies (rack pdus) in the rack.
Rack ATS is usually is supplied by two different rack pdus, so therefore by design (due to power capacity calculations) a server can only be supplied from one inlet when connected to rack-ATS. That's also the notification being displayed for you:
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-06 12:32 AM
Hi Martin,
Amphenol Network Solutions items not included in DCO/ITA Genome Library. You might want to submit a genome request here:
https://helpcenter.ecostruxureit.com/hc/en-us/requests/new?ticket_form_id=360000949677
As a current work-around you might use another network unit (from the Genome Library) and customize it in your Genomes to fit your need - eg. in Genomes you can modify the assets properties (Physical, Power and Network and other settings).
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-12 10:48 AM . Last Modified: 2022-09-12 11:01 AM
Hello @Jef
I need a genome that allows me to establish 2 power supplies (PDU1 and PDU2) and to be able to use this equipment as a power source for other equipment.
The problem I have is the following:
When selecting the source within the equipment it only allows me to select this equipment in only 1 power source and I need to set it in both; below a drawing.
I used the genome 1.4kW Single-Phase ATS / Metered PDU (PDUMH15AT) but was unsuccessful
Do you know any genome that can work for me?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-13 03:05 AM
Hi Martin,
It doesn't seem to be genome related issue, but likely configuration related.
You can connect a server/asset (in 2N redundancy) to both rack pdus (assuming they have proper power configurations setup).
However, if you are connecting a server/asset to a rack ATS, then please note that server can be supplied only from one inlet when the rack ATS is used.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-14 05:52 AM . Last Modified: 2022-09-14 05:53 AM
Hi Martin,
If I understand correctly you want to power your asset from a rack-ats and also from another source (rack pdu /rack ats), right? if yes, then that is not supported.
When we connect a rack mounted item/server with 2N redundancy, then it may/can be connected to 2 different power supplies (rack pdus) in the rack.
Rack ATS is usually is supplied by two different rack pdus, so therefore by design (due to power capacity calculations) a server can only be supplied from one inlet when connected to rack-ATS. That's also the notification being displayed for you:
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-14 07:01 AM
Hi Martin,
My pleasure & you are very welcome.
Kind regards,
Jef