I've recently installed a Demo of Data Center Expert 7.9.2.78. I went through importing the OVA and configuring all the network info in the console. Now I am not able to log into the web interface. I tried "apc / apc" with no success and the other various accounts I had to configure passwords for. Nothing seems to work. Can anyone help?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-11 02:52 PM
There isn't a default user/password in DCE 7.9.2, it would have been one of the first user accounts you create after you log into the linux console with apcsetup/apcsetup. If you reboot the DCE vm, then log into the linux console with the apcreset user, you can create a new admin user for the web interface/desktop client.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-11 02:52 PM
There isn't a default user/password in DCE 7.9.2, it would have been one of the first user accounts you create after you log into the linux console with apcsetup/apcsetup. If you reboot the DCE vm, then log into the linux console with the apcreset user, you can create a new admin user for the web interface/desktop client.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.