Data Center Expert - Configuring alerts to detect a utility outage

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Data Center Expert - Configuring alerts to detect a utility outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All
Related Products
product field
Schneider Electric
Data Center and Facility 3 Phase UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
marlerc
marlerc
Cadet

Posted: ‎2022-10-11 06:28 AM

0 Likes
2
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:28 AM

Data Center Expert - Configuring alerts to detect a utility outage

Description:  We are using Enterprise Data Center Expert with Colo and ITA managing our data centers, multiple regional office server rooms, hundreds of LAN closets, and all sites power is protected with Symettra and SmartUPS.

 

Just like another engineer who relies on Schneider solutions we want to know when utility power goes out and comes back.  This is a fundamental requirement of power protection and monitoring.

See thread: https://community.se.com/t5/EcoStruxure-IT-forum/how-do-I-create-an-alarm-to-show-the-ups-has-no-inp...

 

The problem:  Data Center expert can send an "on battery" alert, but the UPS goes on battery every time it self tests, and there is no ability to qualify the "on battery" state to eliminate alerting on self tests,

Consequently, Data Center Expert routinely sends hundreds of "on battery" alerts to the Enterprise Operations center.  

Rather than launch to each UPS's every time and verify the last transfer to battery was due to a self test, the operators ignore the messages.  

 

Is there any UPS operational or other alert state threshold that will report degraded utility conditions sufficient to transfer to battery?  We really need a better solution than this.  We ARE power monitoring, aren't we?

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2022-10-11 06:46 AM . Last Modified: ‎2022-10-11 06:51 AM

0 Likes
1
1333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:46 AM . Last Modified: ‎2022-10-11 06:51 AM

Hi @marlerc ,

 

You're correct. The UPS goes to battery on a self test and if you're creating a manual threshold, you can not specify conditions such as on battery only when there is no self test. The manual threshold WILL get triggered in this case.

 

If you're using APC Symmetra and Smart-UPS however (and most other 3rd party UPS units for that matter), you should not need to create a manual threshold. As long as there have been no issues during discovery (specifically DDF related errors on APC units), the UPS already has an "on battery" alarm by default:

 

see on-bat.png

there are also other options that may help

see other.png

 

Not sure why they would not properly add as images to the reply.

 

This is the only option that will provide you UPS on battery when it's NOT doing a self test.

 

Thanks,

Steve

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

marlerc
marlerc
Cadet

Posted: ‎2022-10-17 05:26 AM

In response to APC_Steve
0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-17 05:26 AM

To accommodate potential polling cycle delay and to engineer the shortest possible time from utility outage to messaging we are testing  two options:

 

Configuring Data Center Expert, with all the individual UPS scan settings configured to 1 minute and trapping directly

scansettings.JPG

 

 

Also, we are configuring UPS's individually to disable self test emails to operators and email the operator from the UPS itself when on battery in response to utility outage

 

 

 

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of