Posted: 2020-05-22 09:20 AM
A vulnerability Scan has picked up the following Vulnerabilities with my DCO Server v8.0.2 :
I intend to upgrade the Server to DCO v8.3.2 to address certain vulnerabilities however I wish to know if there are certain configurations I need to perfom to address the above mentioned Vulnerabilities or the latest version of DCO has these issues already addressed?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-26 09:54 AM
Hello.
Upgrading your DCO installation should address the security issues you have noted in your post. DCO 8.0.2 is quite old and has received a number of security improvements since that timeframe.
Ciphers are updated and the more recent releases can be configured to accept only TLSv1.2 connections.
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-26 09:54 AM
Hello.
Upgrading your DCO installation should address the security issues you have noted in your post. DCO 8.0.2 is quite old and has received a number of security improvements since that timeframe.
Ciphers are updated and the more recent releases can be configured to accept only TLSv1.2 connections.
Regards
Greg Sterling