DCO User Fails to Log in in Web Client

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO User Fails to Log in in Web Client
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
hranto
hranto Cadet
Cadet

Posted: ‎2023-08-25 01:32 AM

0 Likes
1
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-25 01:32 AM

DCO User Fails to Log in in Web Client

Dear Support, 

 

We have fresh new installation of DCO 8.3.8 and ITA 9.3.11. Both DCOs are freshly installed and users are created with their credentials. 

On first log in, the users are failed to log in. Only root user is accessible and successfully logged in. The admin/web user is failed to log in. 

We checked the user credentials in the webmin in Users and Groups. The password is selected automatically predefined password. Although we modify it to Normal password yet the option resets itself to predefined password. 

Can you kindly advise what could cause this issue and hoe to resolve it?

Thank you in advance,

Best Regards,

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2023-08-27 11:39 PM

1 Like
0
1169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-27 11:39 PM

Hi Hranto,

User(s) created during the installation can only access the server (via server Webmin interface and/or console/ssh login), same goes for users created via the server Webmin interface.

 

ITA application has its own user administration. 

After a successful installation of ITA (or DCO), login to web-client (https://<ITA server IP>) using the default credentials:

Username: apc

Password: apc

you will be prompted to change the password (on first login).
If you need to create new users, then go to Administration > Users , and click on the 'ADD USER' 

It is recommended to create a new user (with admin privilege's) and remove/delete the 'apc' user.

 

Kind regards,
Jef

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2023-08-27 11:39 PM

1 Like
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-27 11:39 PM

Hi Hranto,

User(s) created during the installation can only access the server (via server Webmin interface and/or console/ssh login), same goes for users created via the server Webmin interface.

 

ITA application has its own user administration. 

After a successful installation of ITA (or DCO), login to web-client (https://<ITA server IP>) using the default credentials:

Username: apc

Password: apc

you will be prompted to change the password (on first login).
If you need to create new users, then go to Administration > Users , and click on the 'ADD USER' 

It is recommended to create a new user (with admin privilege's) and remove/delete the 'apc' user.

 

Kind regards,
Jef

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore