DCE and SNMPv3 SHA/AES not working w/ UPS NMC

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE and SNMPv3 SHA/AES not working w/ UPS NMC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Phlerm
Ensign Phlerm
Ensign

Posted: ‎2022-10-10 09:27 AM

0 Likes
7
2767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 09:27 AM

DCE and SNMPv3 SHA/AES not working w/ UPS NMC

Odd issue we are seeing. StruxureWare Data Center Expert 7.9.1.83 cannot communicate with UPS Network Management Cards (v2 and v3) via SNMPv3 when using SHA/AES. NMC software versions are: (NMCv2: 7.0.8; NMCv3: 2.2.1.1). If we change the settings for SNMPv3 to MD5/DES (on the NMC and DCE), then DCE is able to successfully scan the UPS/NMC. SNMPv1 works as well. I have been unable to find a documented bug. We are able to query these devices successfully via SNMPv3 SHA/AES for trending data (Cacti).

 

Other devices like PDUs, IRCs and Galaxy VS UPS systems don't seem to be having any trouble.  Any ideas?

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-10-10 11:00 AM

0 Likes
6
2757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 11:00 AM

Hi @Phlerm,

 

Can I ask:

- Was this configuration working previously?

- How & when were the cards upgraded?

- Can you recall exactly what version NMC you lost communication at?

- Has the DCE been rebooted since you lost communication?

 

Thanks,

  Shaun

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Phlerm
Ensign Phlerm
Ensign

Posted: ‎2022-10-10 11:49 AM

In response to Shaun
0 Likes
5
2752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 11:49 AM

Hi Shaun, thanks for responding,

 

- Configuration was working previously

- Cards were upgraded via Struxureware DCE

- Prior version of NMC3 was 2.0.0.5.  Not sure about NMC2, but it was in the 7.x train

- Yes, rebooted DCE as a troubleshooting step. 

 

- I have also tried removing and re-adding NMCs using SNMPv3.  The device is successfully added to DCE, but is unrecognized and labled as "SNMP Device".  Of course I can always change SNMP settings to correct this (switch to SNMPv1 or SNMPv3 w/ MD5/DES) , but it doesn't follow our security guidelines.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-10-12 04:26 AM

In response to Phlerm
0 Likes
1
2725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-12 04:26 AM

Hi,

 

Just checking in so I'm not leaving you in the dark - I'm trying to reproduce this locally.  It's certainly a supported configuration that's expected to work - obviously monitoring our own network cards is most the point of the platform.

 

If I can't replicate the same I may ask you to get in touch with your local support so we can try to capture the network traffic and see what's missing - but I have the same software and the same cards as you, so I'm hopeful I should be able to replicate.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Phlerm
Ensign Phlerm
Ensign

Posted: ‎2022-10-12 09:26 AM

In response to Shaun
0 Likes
0
2719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-12 09:26 AM

Appreciate the update.  I'll update this post if I come across any information that might help troubleshoot.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-10-14 07:47 AM

In response to Phlerm
0 Likes
2
2696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-14 07:47 AM

Hi @Phlerm,

 

Just wanted to check one detail - if you login to the NMC on the UPS, can it still see the UPS status correctly?

 

Showing up as "SNMP Device" when they're re-discovered is an odd detail that may indicate they have the wrong firmware loaded (for example, PDU firmware on a UPS), and we just want to rule that out.

 

Thanks,

  Shaun

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Phlerm
Ensign Phlerm
Ensign

Posted: ‎2022-10-14 10:32 AM

In response to Shaun
0 Likes
1
2690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-14 10:32 AM

Yes, the card can see the UPS correctly. 

 

Just to clarify, a NMC will only show up as "SNMP device" if I add it w/ SNMPv3 SHA/AES.  If I then change the configuration of SNMP on the NMC and DCE to SNMPv3 MD5/DES, the card will be scanned correctly and the model etc updates as expected. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Phlerm
Ensign Phlerm
Ensign

Posted: ‎2022-10-20 12:03 PM

In response to Phlerm
0 Likes
0
2614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-20 12:03 PM

We noticed that DCE 7.9.2 was released yesterday.  Just for good measure, we updated DCE to 7.9.2 today.  We are still seeing the issue w/ SNMPv3 using SHA/AES.

 

Thanks!

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore