Posted: 2023-04-18 04:22 AM
Dear support,
I have encountered that after upgrading the DCE-7.9.1 to DCE-7.9.2/7.9.3, the UPS Total Output Active Power (Watts) sensors are no longer available (Unplugged). An analysis of the changes to the SNMP DDF file apcsmartups.xml v.129 indicated that since DCE-7.9.2:
The following have been moved to a supplementary DDF (apcsmartups_watts_from_va.xml):
We have chosen to remove these sensors as they have been reported by customers to provide
inaccurate/misleading data. If a customer requests to see the per-phase output power in watts
and it is not supported by the device, they can add apcsmartups_watts_from_va.xml DDF to DCE
in addition to apcsmartups.xml DDF
It's strange that there is no mention of this important change in the release for DCE-7.9.2 or DCE-7.9.3. Furthermore, I could not find the mentioned new SNMP DDF file apcsmartups_watts_from_va.xml on https://ddf.ecostruxureit.com/ (only apcsmartups.xml, for example).
Please help in solving this problem, in the meantime, the solution is to revert to using the SNMP DDF file apcsmartups.xml v.123 from DCE-7.9.1
Very thanks for the support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-24 06:22 AM
Hello Spezialist. We apologize for the delay. Attached is the DDF you are looking for. We will make sure to address the underlying issues you've highlighted.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-22 07:03 AM
Dear support, where can I download the SNMP DDF file apcsmartups_watts_from_va.xml?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-24 09:26 AM
Dear @mwhelihan,
Great -- that's what's needed. Recently checked this new SNMP DDF-file on two different DCE-7.9.3 servers: the result is positive, UPS Total Output Active Power (Watts) sensors are back.
Very thanks for the support.