DCE 7.8.0 Web Client - Home Page Timeout

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.8.0 Web Client - Home Page Timeout
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Venkat
Ensign Venkat Ensign
Ensign

Posted: ‎2020-11-26 12:00 AM

3 Likes
9
3383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-26 12:00 AM

DCE 7.8.0 Web Client - Home Page Timeout

Dears,

 

DCE monitoring systems ideal time out more than 15 minute error appearing. Even after the checked remain active check box, still repeating the Home timeout issue.

 

The screenshot attached for your kind reference.

 

DCE.jpg

 

Please advice.

 

Thanks & Regards,

 

K.Venkat

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2020-11-30 05:06 AM

2 Likes
7
3346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-30 05:06 AM

Hi @Venkat ,

 

This is a known issue and I've reported it to engineering. There is no workaround that I am aware of at this time.
I have added this post to the issue report so that engineering can see that customers still see this as an issue.

 

Thanks,

Steve.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2020-11-26 12:03 AM

1 Like
0
3380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-26 12:03 AM

I have seen this on a number of deployments and would be very interested in the solution also. We have tried different browser without any success.

 

Kevin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2020-11-30 05:06 AM

2 Likes
7
3347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-30 05:06 AM

Hi @Venkat ,

 

This is a known issue and I've reported it to engineering. There is no workaround that I am aware of at this time.
I have added this post to the issue report so that engineering can see that customers still see this as an issue.

 

Thanks,

Steve.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Venkat
Ensign Venkat Ensign
Ensign

Posted: ‎2020-11-30 05:51 AM

In response to APC_Steve
0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-30 05:51 AM

Thanks Steve.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JeroenV
Crewman JeroenV
Crewman

Posted: ‎2023-01-30 12:54 AM

In response to APC_Steve
1 Like
1
2068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 12:54 AM

Hi I am using 7.9.2 and still face this issue. Will there be an update on this status soon?

regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

ManoPenktas
Crewman ManoPenktas
Crewman

Posted: ‎2023-03-26 11:13 PM

In response to JeroenV
0 Likes
0
1990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-26 11:13 PM

Same problem with 7.9.3 .....

Reply

Link copied. Please paste this link to share this article on your social media post.

ManoPenktas
Crewman ManoPenktas
Crewman

Posted: ‎2023-03-28 06:21 AM

In response to APC_Steve
0 Likes
3
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 06:21 AM

Hi, is there any update from engineering regarding the fix ?

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2023-03-28 08:33 AM

In response to ManoPenktas
0 Likes
2
1973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 08:33 AM

Hi @ManoPenktas ,

 

Sorry but no, this issue has yet to be addressed.


Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

JeroenV
Crewman JeroenV
Crewman

Posted: ‎2023-03-28 08:39 AM

In response to APC_Steve
1 Like
1
1970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 08:39 AM

I would expect more effort. This issue is addressed for over 2 years now. At least we should get some feedback what took them so long........

 

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2023-03-29 11:15 AM

In response to JeroenV
0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 11:15 AM

Hi @JeroenV ,

 

I honestly can not speak for engineering specifically on this issue however I do know it is not something that is critical like a vulnerability. I can honestly say that this post is about the only place I've heard people noting this issue and like any other issue, the more people contacting us about an issue, the more likely it is to have the people that make these decisions actually take a look at the issues.

 

What I can say is that after again speaking again with engineering and product management, I am told that a fix for this is in 8.0 which should be released some time in Q2 as at this point. Please note this is just an estimate and release dates can change.

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of