DCE 7.4.3 not receiving updates from monitored devices
  • DCE 7.4.3 not receiving updates from monitored devices
129
72
Posted: ‎2020-09-21 05:35 AM
3578
My client is running DCE 7.4.3 on a physical Enterprise server. They server is a bit old but still functional.
We have an issue where some of the devices have communication issues (communication lost alarms) but physical connectivity is there and we are able to launch to the said devices through DCE. We have confirmed that the SNMP community strings have not changed. And the device credentials are still the same.
There is no firewall in between the server and the devices. All are sitting in one LAN segment. Any ideas what the issue could be?
Regards
Kevin
Replies 8
Posted: ‎2020-09-22 01:39 AM
3560
Hi Kevin,
The first thing I'd recommend is to go to:
http(s)://IP-of-DCE/nbc/status/SnmpWalk
And confirm that the devices are providing the correct answers to the DCE.
-Gavan
Posted: ‎2020-09-28 11:44 PM
In response to Anonymous user
3548
Hi @Anonymous user ,
Is the utility available on 7.4.3 from the web client? I have tried this on my test server and all i get is "The requested URL /nbc/status/SnmpWalk was not found on this server."
Any other suggestions?
Kevin
Posted: ‎2020-09-29 01:46 AM
3543
Hi Kevin,
Sorry, it's not available in 7.4.3, can you try to do an SNMP walk from a different computer?
-Gavan
ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander
Posted: ‎2020-09-29 06:43 AM . Last Modified: ‎2020-09-29 06:45 AM
4
3531
snmp walk from the DCE web client is only available in DCE 7.6 and above.  However you still use the device walk utility found here https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360006388878-How-to-create-a-device-walk-fil...
this will also allow you to walk modbus devices.
out of curiosity, are they snmpv3 devices?  If so, are they APC devices?  If they are, I would recommend making sure they are running the latest firmware.  You may need to reboot the web interface for snmpv3 communication to come back
Posted: ‎2020-09-29 06:54 AM
In response to ATrabert
3524
Thank you @ATrabert
All devices are APC. Ranging from Inrows, rack PDUs and UPS units.
Nothing changed in the environment. They were reporting and they just happened to have lost communication.
A firmware update of the NMCs could assist the issue. I know the firmware has not been getting upgraded.
Kevin
ATrabert
Lt. Commander
Posted: ‎2020-09-29 07:06 AM
2
3520
I would definitely recommend upgrading the firmware regardless then.  Do you know DCE is polling them via snmpV1 or snmpV3?  snmpV1 devices should be fine, but older nmc1 devices running 3.5.x have been known to have issues with snmpv3.
Posted: ‎2020-09-29 07:09 AM
3517
Hi @ATrabert
Oh yes, all devices are monitored via SNMPv1. There is a mixture of nmc1, nmc2 and MGE 66061 cards.
Kevin
ATrabert
Lt. Commander
Posted: ‎2020-09-29 07:21 AM
ok then, if firmware update/nmc reboot does not correct the issue, you may want to check the nmc event logs to see if there are any specific snmp events.