Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Cooling Configuration - Alarm

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Cooling Configuration - Alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Venkat
Ensign Venkat Ensign
Ensign

Posted: ‎2020-07-31 08:35 AM

0 Likes
2
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 08:35 AM

Cooling Configuration - Alarm

Hi team,

 

One of our customer, we need to show the below DCIM Feature points for Cooling configuration.

 

We didn't find out the Alarms / recommended actions as follow up the below scenario. 

 

Ability to alarm cooling configuration issues and provide recommended actions. For example, a room has no perforated tiles for the Computer Room Air Conditioning (CRAC) unit airflow (one or more CRACs have been added to the floor but no perforated tiles have been added), or there is no perforated tile airflow (one or more perforated tiles have been added to the room but no CRACs have been provided to supply any airflow).

 

Kindly suggest us with screenshots to explain customer end.

 

Thanks & Regards,

 

K.Venkat.

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2020-08-02 11:30 PM . Last Modified: ‎2020-08-03 04:55 AM

0 Likes
1
2058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-02 11:30 PM . Last Modified: ‎2020-08-03 04:55 AM

Hi Venkat,

The notification concerning adding perforated tiles may be displayed if there should be modeled downflow CRACS in the room.

Modeling downflow CRACS requires raised floor and adding some perforated tiles.  To configure raised floor, right click on your room/data center > Properties > Floor , and then enable the 'Raised floor' option and define 'Floor height'.

 

In the following illustration I have only modeled a Downflow CRAC:

Capture_1.JPG

then I will go ahead and set the room/Floor properties:

Capture_2.JPG

and add Perforated Floor Tile(s):
Capture_3.JPG

 

Kind regards,

Jef

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2020-08-02 11:30 PM . Last Modified: ‎2020-08-03 04:55 AM

0 Likes
1
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-02 11:30 PM . Last Modified: ‎2020-08-03 04:55 AM

Hi Venkat,

The notification concerning adding perforated tiles may be displayed if there should be modeled downflow CRACS in the room.

Modeling downflow CRACS requires raised floor and adding some perforated tiles.  To configure raised floor, right click on your room/data center > Properties > Floor , and then enable the 'Raised floor' option and define 'Floor height'.

 

In the following illustration I have only modeled a Downflow CRAC:

Capture_1.JPG

then I will go ahead and set the room/Floor properties:

Capture_2.JPG

and add Perforated Floor Tile(s):
Capture_3.JPG

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Venkat
Ensign Venkat Ensign
Ensign

Posted: ‎2020-08-03 08:25 AM

In response to Jef
0 Likes
0
2049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 08:25 AM

Thanks Jef.

 

Simulated with customer exiting solution and got the same result.

 

Regards - K.Venkat

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore