Cooler Capacity Model

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Cooler Capacity Model
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
WeiT
WeiT Cadet
Cadet

Posted: ‎2022-09-23 12:33 PM . Last Modified: ‎2025-04-02 11:30 PM

0 Likes
1
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-23 12:33 PM . Last Modified: ‎2025-04-02 11:30 PM

Cooler Capacity Model

We were recently asked about the cooler capacity model and want to provide some supporting information.
 
According to our experience with data-center cooling design, the majority of cases are not limited by cooler capacity, but instead the cooling airflow that delivers cooling to rack inlets. So, we recommend first trying the infinite capacity model, which allows coolers to always maintain the supply temperature setpoint. If the rack-cooling checks are green, it is likely that the rack cooling performance is fine. To rigorously verify if a cooler is overloaded, one can compare the actual load to the actual cooler capacity, which can be manually determined from the technical data manual with refence to the return temperature.
 
In cases where supply airflow rate is low, such as when simulating cooler control, one may consider the specified capacity model. In reality, the cooler capacity linearly increases along with the return temperature. ITA CFD predicts the capacity at a given return temperature with a linear interpolation using two points provided by the user consisting of a return temperature and capacity, both at the same reference airflow. If the actual load is less than the capacity, the supply temperature setpoint will be kept; otherwise, the supply temperature will be above the setpoint.
 
After the solve, one can always hover the mouse on cooler to find the relevant information, such as actual load, actual cooler capacity, return temperature, and supply temperature.
 
Terminology:
  1. Heat Load, or simply Load, means the amount of heat generated in the whitespace (which is eventually removed by coolers).
  2. Capacity means the maximum amount of load a cooler can remove from whitespace to outside at a certain set of operating conditions.
  3. Supply Temperature means the average temperature of airflow at the supply terminal(s) of a cooler.
  4. Return Temperature means the average temperature of airflow at the return terminal(s) of a cooler.
  5. Supply Temperature Setpoint, or simply Setpoint, means the desired supply temperature set by the user for a cooler. It might or might not be maintained, depending on the capacity and load.
 
Please let us know if you have more questions or comments!
Labels
  • Labels:
  • IT Design CFD
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-04-21 05:18 AM

0 Likes
0
454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-21 05:18 AM

More about EcoStruxure IT Design CFD is coming soon in the EcoStruxure IT Help Center.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore