Hi all,
We have 12 of these PDUs installed in two different server rooms. We also have a couple of temp and humidity sensors (AP9335TH).
Everything is working great, very happy with all the hardware so far.
Question is, is it possible to get reports about temperature and humidity by time periods? Like last 24 hours, week, etc
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-25 06:49 AM
Hello @javiwaku,
The PDU themselves only keep so many entries at a defined interval within the interface. From the PDU itself, you should be able to get the raw data and save it if needed, but this would need to be done 12 times, once for each PDU.
You can use EcoStruxure IT Data Center Expert or EcoStruxure IT Expert to run sensor history reports for sensors over a period of time.
DCE: https://www.se.com/us/en/faqs/FA301697/
These DCIM monitoring tools allow you to aggregate data and easily report on it within reports and dashboards for regular viewing.
Kind Regards,
Cory