Posted: 2025-12-01 11:03 PM
I am looking for the Easy UPS 3M MiBs. I need to import them in snmptrapd.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-03 08:23 AM . Last Modified: 2025-12-03 08:24 AM
Hi @Iqra_shafiq,
Go to the Software and Firmware Downloads page on se.com and search for MIB. You will see the PowerNet MIB.
Easy UPS 3M with the AP9547 NMC3 installed use the PowerNet MIB.
https://www.se.com/il/en/download/doc-group-type/120246296111-Software+%26+Firmware/?keyword=MIB
There is a compatibility chart here to help you see which NMC3 your units have installed: https://www.se.com/us/en/faqs/FA237786/
If your units have an NMC other than AP9547 installed, please contact support for help locating the proper MIB.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-03 08:23 AM . Last Modified: 2025-12-03 08:24 AM
Hi @Iqra_shafiq,
Go to the Software and Firmware Downloads page on se.com and search for MIB. You will see the PowerNet MIB.
Easy UPS 3M with the AP9547 NMC3 installed use the PowerNet MIB.
https://www.se.com/il/en/download/doc-group-type/120246296111-Software+%26+Firmware/?keyword=MIB
There is a compatibility chart here to help you see which NMC3 your units have installed: https://www.se.com/us/en/faqs/FA237786/
If your units have an NMC other than AP9547 installed, please contact support for help locating the proper MIB.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-04 02:55 AM
I was successfully able to download the powernet Mib and it worked fine with my Easy UPS 3M NMC3.