Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unable to change temperature value from F to Celsius

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Unable to change temperature value from F to Celsius
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2020-11-11 06:35 PM . Last Modified: ‎2022-10-19 02:01 AM

0 Likes
11
6449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-11 06:35 PM . Last Modified: ‎2022-10-19 02:01 AM

Unable to change temperature value from F to Celsius

Hi,

 

How do I change temperature sensor value to Degree Celsius in DCO. Currently it is showing Fahrenheit. The temp/humidity sensor is directly connected to RPDU.

 

I saw the topic below, but unfortunately changing the from US to Metric doesn't work for me.

https://community.se.com/t5/EcoStruxure-IT-forum/Temperature-value-setting/m-p/202199#M1593

 

Can you support me on this ?

 

Thank you

 

DCO_Temp.JPG

 

 

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Jef
Jef Leader
Leader

Posted: ‎2020-11-12 12:40 AM

2 Likes
9
6442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-12 12:40 AM

Hi Stefano,

Additional to your illustrated settings (in desktop client, Tools > Preferences > General), measurement units in DCO (and ITA) are appearing according to the settings selected by the operation system on the client's computer. The 'Region' control panel allows user to select these settings:
Capture-jf.JPG

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-12 09:32 AM

In response to Jef
0 Likes
8
6422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-12 09:32 AM

Hi Jef,

 

thank you so much for your suggestion, looks like the settings are the same (except some italian word), it's very strange

cause on the same workstation DCO shows F° and DCE C° 

 

 

DCO.png

 

os_sett.JPG

 

Best regards,

Stefano

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2020-11-13 04:49 AM

In response to Anonymous user
0 Likes
7
6400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-13 04:49 AM

Hi Stefano,

You are most welcome & many thanks for the useful illustrations.
That's a different scenario. The units in the alarm description filed are independent of the desktop settings.
This is the way DCE reports alarms and alarm descriptions to DCO. DCO dose not translate the alarm descriptions and will display as they are. 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-13 05:28 AM

In response to Jef
0 Likes
6
6395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-13 05:28 AM

Hi Jef,

 

ok thanks, should I change switch to METRIC on DCE server in order to see C° on DCO?

 

Regards

 

Stefano

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2020-11-13 05:42 AM . Last Modified: ‎2020-11-13 05:56 AM

In response to Anonymous user
0 Likes
5
6392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-13 05:42 AM . Last Modified: ‎2020-11-13 05:56 AM

Hi Stefano,

Yes, you can try that.

Apparently your DCE server regional settings might be in US or something and you might want to change it to something like English (METRIC).
It can be done via DCE desktop client, System > Server Administration Settings > Time Settings , and then under "Regional Settings" change the Server Local to English (METRIC).

Then the Alarms notifications (reported from DCE) would be in Metric in DCO.

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-17 01:56 AM

In response to Jef
0 Likes
4
6359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 01:56 AM

Hi Jef,

 

great! I tried to set English METRIC but after the server restart the configuration didn't change ( tried 3 times ).

Could be a bug? I will try to upgrade DCE version from 7.7.1.40 to 7.8.0.47, probably it will solve it.

I will update you soon.

 

Regars

Stefano

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-18 01:17 AM

In response to Anonymous user
0 Likes
3
6353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-18 01:17 AM

Hi Crew,

 

I completed the DCE upgrade, but unfortunately the issue is still there.

 

I tried to change locale setting to English Metric or Italian couple of times but after the server restart, English US comes back into configuration menu.

 

Any suggestions?

 

Kind regards,

Stefano

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TechieBala
TechieBala Troubleshooter
Troubleshooter

Posted: ‎2020-11-18 04:43 AM . Last Modified: ‎2020-11-18 05:07 AM

In response to Anonymous user
1 Like
2
6346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-18 04:43 AM . Last Modified: ‎2020-11-18 05:07 AM

Hi @Anonymous user  I just realized that the issue which you want to resolve is on the DCO client for the alarms that are received from the DCE server not on the DCE desktop client itself. As per your screen shot, you are already able to see the DCE temperature unit in Celsius, but you are seeing the temperature alarms in Fahrenheit. Let me also investigate and I will let you know if I find something for you soon. Thanks!

 

Regards,

Bala

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-18 06:19 AM

In response to TechieBala
0 Likes
1
6336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-18 06:19 AM

Hi Bala,

 

thank you so much!

Actually I am able to see C° as shown on the screen shot, because I changed the configuration from DCE client side.

File -> Client Preferences -> Client Language Settings -> Select Language -> English - Metric

 

Server side if I change the time settings in the System menu from US to Metric, after reboot the locale configuration show back US.

Please let me know if your suspicions are well founded... after the investigation on DCO client of course.

 

Regards,

 

Stefano

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TechieBala
TechieBala Troubleshooter
Troubleshooter

Posted: ‎2020-11-22 06:38 AM . Last Modified: ‎2020-11-22 06:39 AM

In response to Anonymous user
0 Likes
0
6283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-22 06:38 AM . Last Modified: ‎2020-11-22 06:39 AM

Hi @Anonymous user I am sorry for the delay. I was able to change the Server Locale to English Metric without an issue in DCE, and then I was able to receive the temperature alarms in Celsius on DCO as well. So It looks like that the issue which you are experiencing needs to be investigated in depth. I suggest you to contact our regional customer care team/FSR to analyze the issue further so that they can collect the required details to provide further recommendation. Thanks for your understanding! 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-25 03:38 AM

0 Likes
0
6262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-25 03:38 AM

Yes, I got the same issues Target EHR

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore