New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Not able to receive alert on DCE for third party device
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-2612:01 AM
Not able to receive alert on DCE for third party device
We have integrarted new third-party environmental sensor (BKT Elektronik), we can able to fetch device using SNMP in DCE, but we are not receive warning or critical alerts on DCE.
Please let us know if we need to import and MIB file to receive alert
Third party devices require the creation of thresholds within DCE to cause alerts. Alerts from the device will not be seen in DCE, only sensor data points that are programmed into the DDF will be seen. You can see what sensor data points are available for the device in DCE by going into the Monitoring perspective, and then right-clicking on the device in device view and selecting View Device Sensors.
After creating thresholds, you will need to add them to a notification policy if you would like to be alerted on alarm conditions: https://www.se.com/us/en/faqs/FA225766/