Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz 755 not posting Surveillance Feed to DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 755 not posting Surveillance Feed to DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Tafadzwa
Tafadzwa
Contributor

Posted: ‎2023-02-27 12:40 AM . Last Modified: ‎2023-03-06 11:27 PM

0 Likes
11
11203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-27 12:40 AM . Last Modified: ‎2023-03-06 11:27 PM

NetBotz 755 not posting Surveillance Feed to DCE

Hi All

 

I have a few NetBotz 755s that I have discovered into DCE however they are not posting any surveillance feed as their Cameras are not showing under the Surveillance Tab.

I followed these steps: Data Center Expert | Discovering a NetBotz 700 Series Appliance | APC Slovakia

However only one unit successfully worked as expected but the other units are still not showing under Surveillance. 

I am running on DCE v7.8.1 and NetBotz 5.3.4.

I have added the DCE Certificate to the NetBotz and vice versa but I am getting the following Alarms:

"Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed."

"Failed to connect to the device API, since the verification of the device's SSL/TLS Certificate has failed. As a result, the device may fail to show any connected cameras."

 

Thank you for your assistance.

 

@Jef 

@APC_Steve 

@gsterling 

@JonPro 

Connecting Devices!
Attachments
  • Tags:
  • dce
  • english
  • netbotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
ERNESTO
ERNESTO
Explorer

Posted: ‎2023-02-28 03:14 PM

0 Likes
1
11171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-28 03:14 PM

Hello, I think that what you need are licenses in the DCE to be able to see the surveillance cameras of the Netbotz part number

SWDCE5NSV-DIGI

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2023-03-06 11:25 PM

In response to ERNESTO
1 Like
0
11156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-06 11:25 PM

Hi Ernesto,

 

I do have enough Surveillance Licences. Its not that I cannot License the Cameras, but the Camera Thumbnails are not showing at all under the Surveillance Tab.

Looking forward to your feedback.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

ERNESTO
ERNESTO
Explorer

Posted: ‎2023-03-07 08:32 AM

0 Likes
0
11142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-07 08:32 AM

I recently did a DCIM installation with Netbotz 750 and what I had to do were these steps, he sent the link, I hope it helps you

 

https://dcimsupport.ecostruxureit.com/hc/en-us/articles/360035600753-Netbotz-750-appliance-discovery...

Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lincoln_Darran
Contributor

Posted: ‎2024-03-11 10:35 AM

0 Likes
5
10582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-11 10:35 AM

It'd be really great if any of the links in this thread actually worked.  I have 755's, I have surveillance licenses. No camera images.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-03-12 01:03 AM

In response to Lincoln_Darran
1 Like
4
10579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-12 01:03 AM

Hi @Lincoln_Darran 

 

What eventually worked for me was selecting No Verification under NetBotz 750 Camera Communication Settings

Device>NetBotz Appliance Communication Settings>NetBotz 750 Camera Communication Settings>Edit Communication Settings>SSL Verify Options>No Verification

Tafadzwa_0-1710230374625.png

It is very important to add the correct credentials under NetBotz Appliance Credentials using the "Superuser" Account and the correct Root Account Credentials under Device File Transfer Settings. You can confirm the Root Password by Login into the NetBotz via SSH.

If this does not work, please respond with Screenshots of the Errors you are getting.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lincoln_Darran
Contributor

Posted: ‎2024-03-22 02:31 AM

In response to Tafadzwa
0 Likes
3
10509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-22 02:31 AM

Still not working. Installed 3 recently. 2 working fine. 

Did a complete factory reset on the 3rd yesterday afternoon. Rediscovered through DCE. Still not appearing in Surveillance. Still no "Netbotz Appliance Configuration" option appearing. All other sensors working fine.  On the device the camera is working fine and generating camera alerts.

 

Even tried using the option to output the config from a known good 755, and importing it into the one with issues.

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-03-22 04:17 AM

In response to Lincoln_Darran
1 Like
2
10505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-22 04:17 AM

Hi @Lincoln_Darran 

 

Can we take the conversation offline?

 

You can send me a direct message.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lincoln_Darran
Contributor

Posted: ‎2024-03-22 06:05 AM

In response to Tafadzwa
0 Likes
1
10394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-22 06:05 AM

Hi @Tafadzwa,

not a problem.  How? Is it easier for you to DM me?

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-03-27 06:08 AM

In response to Lincoln_Darran
0 Likes
0
10343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-27 06:08 AM

Hi @Lincoln_Darran ,

 

I have dropped you a message.

Please check your messages.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lincoln_Darran
Contributor

Posted: ‎2024-03-27 08:26 AM

0 Likes
1
10297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-27 08:26 AM

Found this on another thread.  And it works like a dream. Create a set of credentials for the specific netbotz device...

 

Additionally, I have noticed that in DCE if you have too many wild cards when it comes to this part:

Device menu --> NetBotz Appliance Communication Settings --> NetBotz Appliance Credentials

It may not work. I recommend adding an individual entry with the specific IP of the unit you're having an issue with.

Additionally, if you have added a secondary user and are using that user instead of superuser for the "NetBotz Appliance Credentials" in DCE, please make sure that this user has logged into the NetBotz appliance directly at least once.

 

Thanks @APC_Steve 

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-03-27 11:41 PM

In response to Lincoln_Darran
1 Like
0
10291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-27 11:41 PM

Hi @Lincoln_Darran 

 

I am glad to hear you found a solution.

 

Thank you for the feedback.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore