Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz 250: Need help to determine the future Power Consumption of my Rack Monitor

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 250: Need help to determine the future Power Consumption of my Rack Monitor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-12-18 01:00 AM

0 Likes
18
9902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-18 01:00 AM

NetBotz 250: Need help to determine the future Power Consumption of my Rack Monitor

Hello,

I am working on the estimation of the power consumption of my future Rack Monitor NetBotz 250.

The NetBotz 250 will be equipped with 3 sensors (2 doors intrusion sensors and 1 hygrometry/humidity sensor).

Based on the datasheet I got, I came to the conclusion that the Power Consumption will be around 98.5W. I think this figure is a little bit too high.

Can anybody help me compute this future Power Consumption?

 

I thank you in adance.

Best Regards,

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-01-13 03:02 AM

In response to Anonymous user
0 Likes
1
9660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-13 03:02 AM

Hello,

 

So to conclude, the theoretical consumption of the NetBotz Rack Monitor would be 27.5W.

This needs after all to be confirmed by physical measures, but I cannot perform them.

 

Thank you for everything.

Best Regards,

 

Raphaël

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
Anonymous user
Not applicable

Posted: ‎2020-12-20 11:37 PM . Last Modified: ‎2020-12-22 03:35 AM

0 Likes
16
9864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-20 11:37 PM . Last Modified: ‎2020-12-22 03:35 AM

Today's data centers consume huge amounts of power. Devices have a rating based on the amount of amps they can use or support.  Every rack deployment will have different power needs based on the servers it contains. power and space, not only raising existing costs but potentially constraining future growth.

 

 

 

 

 

tellpopeyes

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-03 11:35 PM

In response to Anonymous user
0 Likes
15
9778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-03 11:35 PM

Hello,

Happy New Year !

 

So are you saying that the figure I have found does not seem too high ?

I admit I have some reserves because this would mean that the NetBotz has a power consumption higher than a 24-ports Ethernet Switch used at full capacities.

Regards,

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 12:28 AM

In response to Anonymous user
0 Likes
14
9761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 12:28 AM

Hi Raphaël,

 

Ignore the previous post, I've flagged it as spam.

 

I would put your power use at sub 25 watts, the easiest way to know is to temporarily connect a power monitoring device, (I have a few household smart plugs with the feature built in.)

 

I don't recommend using a metered PDU as the power consumption of the 250 is so low it falls below the PDUs margin of error.

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 01:23 AM

In response to Anonymous user
0 Likes
13
9759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 01:23 AM

Thank you Gavan.

I would like to know how you computed the 25W.

 

Regarding the power consumption measures, I am not sure I have such a monitoring device.

I will have to look into that.

 

Regards,

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 01:33 AM

In response to Anonymous user
0 Likes
0
9755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 01:33 AM

It's not something that I worked out...

 

I just know from experience and reading enough technical documents. 😅

 

Devices like that are easy to come by, this is not a recommendation but I personally have a TP-Link HS110 with that feature (25 euro), there is also far more accurate devices but the power consumption of a nb250 is so low that it could be a rounding error in most environments.

 

-Gavan 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2021-01-05 01:59 AM . Last Modified: ‎2021-01-05 02:08 AM

In response to Anonymous user
0 Likes
11
9750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 01:59 AM . Last Modified: ‎2021-01-05 02:08 AM

Hi Raphaël,

 

The manual for this product gives the maximum inlet current (page 27) as "10A (Defined by Switched Outlet Load + 0.25A)" - so that's 0.25A for the bot itself, plus up to 10A for the switched outlet (obviously entirely dependent on if/what load is attached to that outlet).

 

So I'd also assume 25-30W, depending on whether they've reached that 0.25A at 100V (the lowest input the bot is rated for) or 120V (US typ line voltage).

 

It should be noted all figures given in the manual are maximums and not typical consumption.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 05:18 AM

In response to Shaun
0 Likes
10
9746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 05:18 AM

On my side, I found 98.5W

Because I considered:

  • Power consumption of the Rack Monitori NetBotz alone: the 0.25A consumed at 250V (I am in Europe)
  • Power consumption of 3 sensors: 1A consumed at 12V by the outputs

0.25A x 250V + 3 x (1A x 12V) = 98.5W

 

Does it mean I should not consider a potential additional power consumption of the sensors, when I compute the power consumption of the NetBotz fully equipped/connected ?

 

Best Regards,

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 05:28 AM . Last Modified: ‎2021-01-05 05:30 AM

In response to Anonymous user
0 Likes
0
9743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 05:28 AM . Last Modified: ‎2021-01-05 05:30 AM

Hi Raphaël,

 

Power in Europe is normalized at 230v but unless your in the UK (where it's 240v) it's actually 220v.

 

The point that Shaun was trying to make is that the bot is rated for .25A because it can work at both 110v and 230v.

 

Maximum power consumption and actual power consumption are not the same thing.

 

For example:

I have a 500w PSU in my computer but it only pulls 300 watts at full load and 90% of the time it pulls closer to 60w.   

 

I really don't think a sensor consumes 12 watts either.

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2021-01-05 07:14 AM

In response to Anonymous user
0 Likes
8
9738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 07:14 AM

Hi,

 

I'm curious where you'd seeing 1A per sensor?  The only value I see that resembles this is 1A@30V on the output relays - which isn't their consumption, it's the switching capacity.

 

I would assume the 0.25A at the inlet to be the entire power budget, as anything it consumes (or supplies) has to come in through that inlet, so will contribute to the maximum.

 

(Personally I wouldn't assume it consumes 0.25A at 250V either, else it'd consume 0.625A at 100V and the listed maximum would be wrong - but I realise that unless we can provide an actual figure in watts, all we can do is a worst-case with the numbers provided)

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 08:28 AM

In response to Shaun
0 Likes
7
9732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 08:28 AM

I guess I have read it wrong. I mixed up the 12Vdc with the 30Vdc associated to the outputs.

 

I do agree with you that nothing is better than measuring it on the Rack Monitor. However, I cannot do such a thing at the moment. I do not have the tools, nor the ability (thanks CoVid) to measure it.

Therefore, I need to compute it. This is true that I have to put myself into a worst case scenario.

Therefore, it means that the values indicated (0.25A @230V) are for the NetBotz alone, while the 1A @30V are for each output (sensors output).

But 147.5W is too high and not realistic. It is almost equivalent to a Power Consumption of a high performance signal processing computer...

 

On the other hand, I am fearing that only considering 025A @230V might be, in the long run, underestimating the real power consumption of the NetBotz 250, and therefore under dimensioning my Power Distribution Unit.

 

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-05 08:42 AM

In response to Anonymous user
0 Likes
0
9730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 08:42 AM

Sorry Raphael but I have to disagree with how your looking at this, because the bot works on both 230v and 110v the you need to count the maximum power draw as this:

 

110v x .25A or 220 x .125A which is 27.5 watts maximum.

 

The sensors are not separate to that all sensors have to come from with-in that power budget.

 

I'm not sure where your getting the idea that they are 1A sensors more like .1A (100mA) at the most, but regardless the device can not exceed 27.5 watts.

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2021-01-05 09:26 AM

In response to Anonymous user
0 Likes
5
9728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 09:26 AM

Hi,

 

I'm not sure if I was clear on the sensor output - the rating of 1A @ 30V is a relay output.  It's essentially a dry contact - 1A@30V is what you should expect to be able to pass across it without damaging it.  It's not providing or consuming that 1A, it's just promising to safely switch it.

 

Unfortunately I can't visit our bots either right now - I'm quarantined due to christmas travel.  But from what I know of the platform the 250 is built on, I'd estimate it in the ballpark of 10W for the bot itself, another 2x4W for up to 2 connected pod150's (before you need to externally power the pods), and loose change in ancillary sensors (most sensors are 4-20mA, nowhere near 1A).

 

I will look for something more definitive, but we can't just add up every number on the sheet without accounting for where they come from.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-06 12:58 AM

In response to Shaun
0 Likes
4
9720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 12:58 AM

Thank you for your replies.

So, if I understand it well, the power consumption of the Rack Monitor NetBotz 250 is 0.25 x 110 = 0.125 x 220 = 27.5 W

 

@Shaun : I am sorry, but I am not sure to have understood what you explained about the sensors. Sadly, the power consumption is not present on the sensors datasheets. I must rely on the document presented by @Anonymous user 

 

I do agree that the objective is not to add all the figures present on the datasheet, but I do not want to underestimate the power consumption of fully equipped NetBotz with its Sensors.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-06 01:11 AM

In response to Anonymous user
1 Like
3
9717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 01:11 AM

Yes, the maximum power consumption of the device is 27.5 watts.

 

In reality it's power consumption is far lower, even with every sensor port full, sensor pods added and the every feature turned on the device can not exceed 27.5 watts.

 

That is for the device itself, the switched outlet has a capacity of 10Amps, so 2.2KW (I don't recommend running any electrical devices at their maximum) but that is not consumed by the bot, that is just the maximum amount of power that can be made available for a device connected to the outlet. 

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-06 01:39 AM . Last Modified: ‎2021-01-06 01:40 AM

In response to Anonymous user
0 Likes
2
9715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-06 01:39 AM . Last Modified: ‎2021-01-06 01:40 AM

So the Rack Monitor NetBotz consumes 27.5W

However, I will not use the second outlet on the NetBotz. I will use three Ethernet Sensors (2 doors detection and one humidity/temperature sensors). Therefore, I think they will not consume 2.2KW.

However, what will their consumption be ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-13 03:02 AM

In response to Anonymous user
0 Likes
1
9661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-13 03:02 AM

Hello,

 

So to conclude, the theoretical consumption of the NetBotz Rack Monitor would be 27.5W.

This needs after all to be confirmed by physical measures, but I cannot perform them.

 

Thank you for everything.

Best Regards,

 

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Rvphilip
Rvphilip
Explorer

Posted: ‎2021-12-15 11:22 AM

0 Likes
0
6870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-15 11:22 AM

You need to know the useable Square Footage of your facility and the Power Supply for each Server (Server Watts). You will also need to find out your Facility Voltage (VAC), which will likely be 120V or 240V. Next, you need to determine the Number of Racks and the number of Servers Per Rack. Also, I believe there is a calculator for this as I  remember when I was working on a chatbot development services project I calculated the estimated power consumption of my system using the calculator. The first and easiest calculation you need to make is Amps per Server, which will help you calculate the overall power draw per server. To do this, simply divide your Power Supply for Servers (Server Watts) by your Facility Power (VAC).

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-11-25 04:06 AM

In response to Anonymous user
0 Likes
0
5909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-25 04:06 AM

Yes. Sound right.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore