Posted: 2020-08-04 03:28 AM
My DCE (ver 7.8) detect my new nb750 ( ver 5.2.2.63) but receive that error Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed
Credentials are correct, ports are open in the network
How can solve it?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-26 03:00 AM . Last Modified: 2020-08-26 03:12 AM
Dear @masolans
I have seen this error occurs for the two reasons mainly:
Using Netbotz 750 superuser account password instead of appliance's root account password in Device File Transfer Settings
Using the wrong protocol ie., FTP instead of SCP
Please also refer this k-base docs that can be useful for this DDF error.
https://www.se.com/us/en/faqs/FA381605/
https://www.apc.com/au/en/faqs/FA177004/
If possible, please verify these settings again and re-discover the Netbotz 750 appliance in DCE. Please also make sure that you are able to ping the Netbotz appliance IP address through DCE web UI --Status--Additional Information--Troubleshoot network--Ping. If this fails and if DCE can not ping the device, I recommend allowing ping on the device / network where applicable and see if it helps.
I hope this helps.
Regards,
Bala
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-26 03:00 AM . Last Modified: 2020-08-26 03:12 AM
Dear @masolans
I have seen this error occurs for the two reasons mainly:
Using Netbotz 750 superuser account password instead of appliance's root account password in Device File Transfer Settings
Using the wrong protocol ie., FTP instead of SCP
Please also refer this k-base docs that can be useful for this DDF error.
https://www.se.com/us/en/faqs/FA381605/
https://www.apc.com/au/en/faqs/FA177004/
If possible, please verify these settings again and re-discover the Netbotz 750 appliance in DCE. Please also make sure that you are able to ping the Netbotz appliance IP address through DCE web UI --Status--Additional Information--Troubleshoot network--Ping. If this fails and if DCE can not ping the device, I recommend allowing ping on the device / network where applicable and see if it helps.
I hope this helps.
Regards,
Bala
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-03 03:36 AM
@TechieBala Thanks for the information,
I am also facing the same problem, as mentioned in the @masolans statement,
I have done the changes Root, and SCP settings etc. as per your reply but there is still the error persist,
I also upload the Updated DDF files from the https://ddf.ecostruxureit.com/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-03 03:54 AM
@Anonymous user
please try to ping from DCE Server to Netbotz750 IP.
If its not pinging enable/allow "icmp" in your firewall from DCE Server IP to Netbotz750 IP.
Hope this helps.
Thanks
Shemil
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-03 05:13 AM
Hi @Anonymous user May I know the firmware version of Netbotz 750? Is it 5.2.2 or 5.2.3? Are you trying to discover it first time on DCE?
Note: The DDF file that you downloaded is different from scanner DDF. DDF needs to download the scanner DDF file from the device during the discovery process. If it fails, then DCE shows this error.
If the issue still persists, then I suggest you to contact your regional CCC technical support team as they can guide you to resolve this issue.
You can find the contacts in the below link:
https://www.apc.com/us/en/country-selector?ref_url=/in/en/support/contact-us/
Regards,
Bala
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-18 07:10 AM
Hi,
We are also having this problem brand new DCE running 7.8.0 and brand new Netbotz 750 running 5.2.2. Is 5.2.3 available? If so where can I download it from?
We are on a private open network with no firewall and have added root credentials to the Device File Transfer Settings, under SCP only, and superuser login details under the Netbotz Appliance credentials
I have added numerous 750's to DCE's before with no problem. Is it something in the firmware?
Let me know
Kind Regards
Martin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-19 02:03 AM
Netbotz 5.2.4 can be downloaded here:
https://www.se.com/uk/en/download/document/APC_SFNBZ_524_EN/
DCE 7.8.1 has also been released, contact your local support team for the link.
-Gavan